Dec 14, 2013Explorer III
Why do battery needs a float current?
I mean, when it's full, floating and there are no loads?
To fight the self-discharge, alright. But it draws a bit more than self-discharge would require.
I have 300 AH AGM bank, self-discharge is 3% a month - I checked. This is 0.3 AH per 24 hours. So at the end of the solar charging day this is what I should see on the controller display - 0.3 AH. Instead, even after a week of floating, the controller reports ~2 AH gone into the battery by the evening, with average current ~0.3A.
Alright, 20% on heat and other chemistry loss - should still be mere 0.36 AH daily total. Where did other 1.5 AH go? My wiring from charger to battery is temporary 10ft gauge 8 booster cable, but the current is negligible too. Again, - there are no loads, parasitic or other, the bank is disconnected from everything but the charger.
To fight the self-discharge, alright. But it draws a bit more than self-discharge would require.
I have 300 AH AGM bank, self-discharge is 3% a month - I checked. This is 0.3 AH per 24 hours. So at the end of the solar charging day this is what I should see on the controller display - 0.3 AH. Instead, even after a week of floating, the controller reports ~2 AH gone into the battery by the evening, with average current ~0.3A.
Alright, 20% on heat and other chemistry loss - should still be mere 0.36 AH daily total. Where did other 1.5 AH go? My wiring from charger to battery is temporary 10ft gauge 8 booster cable, but the current is negligible too. Again, - there are no loads, parasitic or other, the bank is disconnected from everything but the charger.