- BurbManExplorer III
smkettner wrote:
Why not pull 120/240v service off the existing circuit?
At least double the power and much less effort.
Why not give him a can of gas and some matches?
The existing service is a 30A/120v circuit. 30A requires #10, but they used #8 when installed because of the distance.
If you are suggesting that he split that hot leg into 2 to create 30A/220v, he will overload that neutral and cause a fire.
A 50A RV plug uses a 240v feed from the panel but splits it into two 120v circuits at the RV. You need FOUR conductors: 2 hot legs at 120v each, a neutral and a ground.
Hence the 3-conductor alum wire the OP has will not in any case. - wa8yxmExplorer III
tvman44 wrote:
I guess you could, but I would not use aluminum wire at all. #6 aluminum wire is too small I think for 50 amps.:E
Second. #6 copper might be enough but for a 100 foot run, If you are going to be getting close to 50 amps, consider #4,, let me look up some numbers. 36 Copper has about .04 Ohms per 100 foot. (.08 when you run it back) so at 50 amps that's 4 volt drop in the loop.
#6 Aluminum is .. Far Lossier.. (Frankly I did not find a chart for Aluminum wire) plus you need special connectors on each end to make sure it does not get much worse very fase.. I'd not use Aluminum wire. - Why not pull 120/240v service off the existing circuit?
At least double the power and much less effort. - Grey_MountainExplorerThe short piece consists of three wires. Two are #2, the other is #4. This is what it says on the wire:
2 AWG AL USE-2 600 VOLTS
and
4 AWG AL USE-2 600 volts.
The long piece is also three wires:
6 AWG AL USE-2 600 VOLTS
Currently, there is a four-wire shielded 8 AWG buried cable running from the breaker box to the barn where I keep the RV. I have a 30 amp 110v hookup on that. That cable was there when we bought this place almost 30 years ago.
GM - MEXICOWANDERERExplorerYou need to follow a very specific protocol when using aluminum conductor. The lists of Do's and Don't Do's is long and sometimes arbitrary. Cheat on just one of the points and you will have a fire. Aluminum is satisfactory when installed absolutely to code. BUT BUT BUT I do not see a satisfactory way to join AL to Cu at the female 50 ampere RV socket.
MM49 wrote:
You might want check again. All of the answers are wrong.
MM49
Wire Size Calculator
Careful with that calculator. Copper, single phase, 240v, 50 amp, 10 feet = #14 wire :E- MM49Explorer
- hughesjm21ExplorerI hope you are not thinking that you need 220v for an rv. They use 120 v , 50a.
- MrWizardModeratorThe #6 Alu is too small, I would not use it
#6 copper is used for 50 amps
Either use #2 Alu all the way or use copper all the way, - BurbManExplorer IIIThe minimum wire size for 50A is #6, so you would need a minimum of #6/4 to run a 220v circuit (4 conductors, two hots, neutral, gnd). For a run over 100' long it is advisable to increase the wire size to minimize voltage drop, so you should be looking at #4 copper wire. Aluminum requires upsizing the gauge over copper, so you would need #2 aluminum. So # 2 AL would be OK but #6 AL won't cut it for 50a service. Also agree with others, copper is preferrred over alum.
About Technical Issues