jch2122 wrote:
Neal B. wrote:
Have you checked the ground fault breakers on one of the outlets? Usually in the kitchen or bathroom. Don't forget the breakers in the electrical center.
Yeah, I tried both of those. Could it possible be fuses? They are on opposite sides of the camper though.
No, it wouldn't be fuses. Your outlets are 120 volts and protected by circuit breakers.
Did you reset your ground fault receptacle ?
1. Hopefully you know that when a breaker trips it doesn't go all the way off. If not go back to the breakers and make sure to turn each one off, (completely) and then back on and then see if those outlets are not hot again.
2. If you are still in the same boat test every one of the breakers as follows: with the breaker turned on, put one lead of a test meter on the lug of the breaker that has the black wire on it and at the same time put the other lead of the meter on the neutral bus, (the silver bar with the white wires) - You should get a 120 volts. If not, you have a defective breaker and it needs to be replaced.
3. If all your breakers test good, you either have a broken/lose wire/bad receptacle on one of them or in between, and you need to do a bunch more trouble shooting. If you can't do it yourself, it is time to call an electrician
Jack L