A tripped GFCI is usually what causes this and as said, they can be hidden in unlikely places. But if the receptacles started working again without doing anything, it's not a tripped GFCI.
It could be a loose wire at the converter panel, either the connection to the breaker or to the neutral bus. Not all that uncommon.
I have seen a wire on the rear of a receptacle almost barely hanging on. RVs and mobile homes use a self-contained device ("SCD") receptacle (or switch). The hot, neutral and ground are pushed onto a pair of fingers/slots on the rear. It is supposed to be done with the correct tool but I'm not sure if all electricians at the factories use them or if they are just sloppy (wouldn't be a surprise).
It is also conceivable that you have a hot or neutral wire that is just barely touching the finger on the back of a SCD and travelling is causing it to make or break contact.
Tracking down any intermittent electrical problem can be difficult. If it is intermittent, I would definitely try and find the cause as it could potentially be unsafe. If you can catch it when it's not working, do the following.
As mentioned above, a non-contact voltage tester (or "NCVT" for short)would be a good diagnostic tool for this. See photo below. IIRC, they're around $20 at places like HD. Remove the cover off the converter panel. First check for a loose hot or neutral wire by visual inspection and wiggling the wires. If that looks okay, use the NCVT to verify that the hot (black) wire out of each breaker is working. A voltmeter can be used to see if the power stays on for each circuit in the panel as you wiggle the neutral wires. Use insulated pliers.
If the panel looks okay, then what I would do is systematically pull one receptacle out of the wall at a time and inspect the connections at the rear of it. There are wings that hold the receptacle to the wall and the cover on the rear just pops off. Use the NVT to see if the incoming and outgoing wires are all live. Then with the power off, visually inspect the connections to the fingers. If there is a loose or improperly terminated wire, it will be obvious.
If you can't catch it when it's not working, then I would check the panel as above and then pull out one receptacle at a time and visually inspect the connections.