As a DIY I paid $1450 for 750W in 2014 for all of the parts including UV wires, aluminum for mounting and SS screws and bolts, etc. This included a high end Morningstar MPPT 60 controller. All panels in series which provides much better shade performance than parallel panels, but that is a whole different topic.
For shaded conditions parallel is superior. In series shading one one panel affects all the panels. In parallel it only affects the shaded panel.
I should have added that serial is superior when the panels have bypass diodes. Virtually all larger panels have bypass diodes. This may not apply to some 12V panels.
My 3 serial panels (90V total) have 3 bypass diodes each. Each diode will bypass 20 cells (10 volts) of my 60 cell panels when there is a shadow on that portion of the panel. So basically I have 9 serial panel sections. When 1 section has a shadow for example the diode causes a short which is 0 volts and passes the full amps of the other 8 sections. So the result is (90V-10V) * 8A (panel Imp) or 8/9 of the panels power.
The same panels in parallel result in 1/3 power loss, hence the voltage is lower than the other 2 panels. The result is the power is 6/9 of the 3 panels vs the serial 8/9 of the 3 panels.
In the past I've posted graphs showing the effect of bypass diodes. It's easy to see the 10V steps with full amps for the given sun condition on leafy shade, hard shade and other types of shade.
From past comments I'm aware that panel bypass diodes with serial panels and shade and not well understood. But with some electrical knowledge and research what I've posted can be verified.