When you say that you checked the GFI and there's no voltage, where are you checking? In the plug, or on the wires going TO the plug?
My GFI was tripped, killing the entire circuit which fed 6 outlets. Wiring ran from the breaker panel to the GFI in the bathroom, from there to an outlet by the bedroom sink, from there to an outlet down below the sink in my wetbay, and from there back to the kitchen counter outlet, from there down below the cabinets to feed my converter, and from there to the last outlet in the circuit, right below the kitchen cabinets in my basement bay. THAT last outlet was filled with water/corrosion.
Once I disconnected the outlet (keeping wires separated) I could reset the GFI and all was good.
I replaced the outlet and everything has been fine since.
The point is that if you have a bad outlet/short further down the chain, and you install a new GFI, it won't energize until the problem is fixed. It was easy to figure out which wires were the "feed" wires on my GFI when I took it out of the wall. If I disconnected the wires that were leaving the GFI for the next outlet in the circuit, it would energize, so I knew the fault was further down the line.
So kill the breaker feeding the GFI, then pull the GFI back out and disconnect the wires leaving the GFI for the next outlet, then energize the breaker and see if you can reset the GFI. If you can, like I said, it's further down the line.
Jim
2005 Pace Arrow 36D
Very Understanding Wife
1 Boxer ๐
3 Maine Coon cats