โApr-10-2016 10:17 AM
โApr-13-2016 04:44 PM
CharlesinGA wrote:
In the graphic above, replace the 10 ohm and 30 ohm resistors with something like a 1000 watt microwave, and a 300 watt heater element in the absorption fridge. If you have two exactly identical loads on opposing hots, they you won't see the effects of a open neutral, but since this is impossible, any imbalance of loads causes one side to be high and one to be low voltage.
At home, in an RV or anywhere, and open neutral is the biggest hazard you can encounter in electrical circuity, as far as damage to your appliances and devices.
Second to that would be surges, from lightning strikes or shorting of power company equipment.
Charles
โApr-13-2016 04:43 PM
dougrainer wrote:larry cad wrote:dougrainer wrote:
Lets handle some misstatements here.
220 versus 120. Well, for RV's below 500K, this is a non issue. It allows smart alecks to tout their limited knowledge when they claim YES, there is 220(240) to the RV. Technically, yes. But the systems are built and separated that ONLY 120 volts is in the RV. ALL the claims of 220(240) do is make people think they have that when they do NOT. It just confuses them. They always tout the HI LINE RV's that have 220 dryers and such. Well. this forum is not about Hi line RV's, it is for the 99 percent that are under 500K. People that have million plus RV's do not read these forums and they certainly do not attempt to repair problems themselves. Doug
Sorry Doug, I have to disagree with you.
I am "IN" my RV. I am in the bedroom of my RV. My RV is not a "hi line", and no where near $500,000, and I fix my own RV. I am not a smart alec, and I DO know what I am talking about because I do electricity for a living, and I spent several years gaining a degree in electrical engineering just to back it up, so please don't tell me that there is no 240v in my RV and please don't confuse the issue more than it already is by making additional misstatements.
The real confusion happens when people don't understand the difference between 50 amp RV service and 30 amp RV service. However, the 240v that is in the RV can be a real problem is there is a loose neutral, for example.
Not trying to cause trouble, just trying to clear up an ongoing problem.
THIS IS WHAT I POSTED. NEVER said there was NOT 220/240. Doug
"YES, there is 220(240) to the RV. Technically, yes. But the systems are built and separated that ONLY 120 volts is in the RV"
โApr-13-2016 04:29 PM
โApr-13-2016 02:37 PM
larry cad wrote:wa8yxm wrote:rgatijnet1 wrote:
In my house, the neutral and ground are tied/bonded together in the main electrical panel. In the RV, the neutral and ground are not tied together in the main panel.
This is not true.. When you plug into the park pedistal, they are bonded, your RV is considered a "Sub Panel" I know exactly where mine is bonded 7 sites west of me (where the main panel is).
However it is true that when you are not plugged into a properly wired outlet,, Yes, then they are not bonded. This often includes both Generator and inverter power.. They may or may not (usually not) be bonded. My inverter is bonded if inverting. Not if Generator is in use.
But the RV is a "Sub" panel off the park main, and it's the park main where the bonding happens.
You should re-read what the this person said.
โApr-13-2016 05:13 AM
larry cad wrote:dougrainer wrote:
Lets handle some misstatements here.
220 versus 120. Well, for RV's below 500K, this is a non issue. It allows smart alecks to tout their limited knowledge when they claim YES, there is 220(240) to the RV. Technically, yes. But the systems are built and separated that ONLY 120 volts is in the RV. ALL the claims of 220(240) do is make people think they have that when they do NOT. It just confuses them. They always tout the HI LINE RV's that have 220 dryers and such. Well. this forum is not about Hi line RV's, it is for the 99 percent that are under 500K. People that have million plus RV's do not read these forums and they certainly do not attempt to repair problems themselves. Doug
Sorry Doug, I have to disagree with you.
I am "IN" my RV. I am in the bedroom of my RV. My RV is not a "hi line", and no where near $500,000, and I fix my own RV. I am not a smart alec, and I DO know what I am talking about because I do electricity for a living, and I spent several years gaining a degree in electrical engineering just to back it up, so please don't tell me that there is no 240v in my RV and please don't confuse the issue more than it already is by making additional misstatements.
The real confusion happens when people don't understand the difference between 50 amp RV service and 30 amp RV service. However, the 240v that is in the RV can be a real problem is there is a loose neutral, for example.
Not trying to cause trouble, just trying to clear up an ongoing problem.
โApr-12-2016 06:13 PM
DrewE wrote:wa8yxm wrote:
However it is true that when you are not plugged into a properly wired outlet,, Yes, then they are not bonded. This often includes both Generator and inverter power.. They may or may not (usually not) be bonded. My inverter is bonded if inverting. Not if Generator is in use.
But the RV is a "Sub" panel off the park main, and it's the park main where the bonding happens.
For a built-in generator in an RV, neutral and (chassis) ground should be bonded together per the NEC, as I understand things. If it isn't, then the installation isn't quite right. On my motorhome. they are indeed bonded at the generator by having the ground and neutral leads from the generator connect to the same star-shaped connection doohicky on the generator chassis (which is also where the 12V chassis ground return line is connected).
On a (small) portable generator, neutral and ground are generally not bonded together, I suppose because sometimes these will be hooked up to a household electrical distribution system and having two neutral/ground bonds is to be avoided.
โApr-12-2016 04:37 PM
wa8yxm wrote:
However it is true that when you are not plugged into a properly wired outlet,, Yes, then they are not bonded. This often includes both Generator and inverter power.. They may or may not (usually not) be bonded. My inverter is bonded if inverting. Not if Generator is in use.
But the RV is a "Sub" panel off the park main, and it's the park main where the bonding happens.
โApr-12-2016 04:07 PM
wa8yxm wrote:rgatijnet1 wrote:
In my house, the neutral and ground are tied/bonded together in the main electrical panel. In the RV, the neutral and ground are not tied together in the main panel.
This is not true.. When you plug into the park pedistal, they are bonded, your RV is considered a "Sub Panel" I know exactly where mine is bonded 7 sites west of me (where the main panel is).
However it is true that when you are not plugged into a properly wired outlet,, Yes, then they are not bonded. This often includes both Generator and inverter power.. They may or may not (usually not) be bonded. My inverter is bonded if inverting. Not if Generator is in use.
But the RV is a "Sub" panel off the park main, and it's the park main where the bonding happens.
โApr-12-2016 04:02 PM
dougrainer wrote:
Lets handle some misstatements here.
220 versus 120. Well, for RV's below 500K, this is a non issue. It allows smart alecks to tout their limited knowledge when they claim YES, there is 220(240) to the RV. Technically, yes. But the systems are built and separated that ONLY 120 volts is in the RV. ALL the claims of 220(240) do is make people think they have that when they do NOT. It just confuses them. They always tout the HI LINE RV's that have 220 dryers and such. Well. this forum is not about Hi line RV's, it is for the 99 percent that are under 500K. People that have million plus RV's do not read these forums and they certainly do not attempt to repair problems themselves. Doug
โApr-12-2016 02:31 PM
rgatijnet1 wrote:
In my house, the neutral and ground are tied/bonded together in the main electrical panel. In the RV, the neutral and ground are not tied together in the main panel.
โApr-12-2016 08:23 AM
FIRE UP wrote:kuzined wrote:
Have a 2005 Pacearrow gas.Is there a converter on this rig and if yes where would it be.Also, when the rig is plugged into 50amps,how is the power separated between 220 and 110? Does the converter do this?Problem Im having is this morning the power went off in my rig. The park pedestel was ok but the fuse blew on my fridge, and the convection microwave quit. I think it got fried.It also shut the gfi down in the bath which killed the power for the plugins.Park says if there was a power surge, the main breaker on the pedestel would shut down.They say its probably the converter that causede all the headache. Are they right? thanks
Well Sir,
First off, since your coach is a gas coach, yes, it will most likely be fitted with a converter. Second, NO, there is no 220VAC that enters your coach. Just because you're plugged into a 50, it doesn't mean you're receiving 220V. Yes, the plugs and the way it's wired, is very similar to 220VAC but, in all reality, it's two, 120VAC lines entering your coach.
Your converter accepts that and, takes care of all the distribution of that 120VAC throughout the coach. All of us in the RV planet, fear the dreaded "power surge" from RV parks and camp grounds. Many have taken steps to prevent potential damage from those surges by purchasing ultra heavy duty surge protectors, sold on line, in RV Parks, RV Parts Suppliers like Camping World and many more places.
And those surge protectors range anywhere from around $50.00 to, around $400 or so, depending on the level of protection and, all the other bells and whistles that one would want on it.
I'm not anywhere near an electrical expert but, I'd bet dollars to donuts that your converter did not trip the pedestals power supply but, what do I know?
As far as where is your converter, well, you'll have to trace the incoming wire (shore power cord) to see where it leads you after it enters the coach. Or, consult your owners manual or, get a hold of the manufacturer of your chassis or coach and see if you can obtain info on the locale of that converter. They seem to put those converters in some odd places in some of the gas coaches.
If your GFI has tripped, there's at least two reasons. One, the norm, is that you have or had, a short some place that may have be in the lineup of what that GFI controls. The second reason is, those GFCIs can get weak over time and, if you breath on one, it will trip. I've had to replace a couple of them, due to the fact that they were just weak.
But, in any case, it sounds as if your coach may in need of some electrical inspection and maybe some maintenance or repair. Good luck.
Scott
โApr-12-2016 08:18 AM
larry cad wrote:rgatijnet1 wrote:
In my house, the neutral and ground are tied/bonded together in the main electrical panel. In the RV, the neutral and ground are not tied together in the main panel.
That is because (by National Electrical Code), the breaker panel in your house is a "main" panel, while the panel in your RV is classed as a "sub-panel". There are very different requirements for handling the ground and the neutral in a sub-panel. The "bond" to which you referred is in the main panel in the campground. You are a sub-panel to that main panel.
โApr-12-2016 08:10 AM
rgatijnet1 wrote:
In my house, the neutral and ground are tied/bonded together in the main electrical panel. In the RV, the neutral and ground are not tied together in the main panel.
โApr-12-2016 08:04 AM