Sudden Hot & Ground Rev per Southwire Receptalce Tester

SpaceCoast_Fan
Explorer
Explorer
Spent the afternoon on regular exercising of generator, running AC and watching TV on my 2013 Thor Freedom Elite 23U. Suddenly the TV goes out. I test all outlets in RV. Only two outlets read Hot & Ground Rev per above tester, TV and refrigerator. Other GFIC outlet in bathroom, dining room and entryway tests correct. What would cause this sudden change in current? Thanks in advance for any help.
7 REPLIES 7

cavie
Explorer
Explorer
ndrorder wrote:
Just a big guess that may be the circuit breaker tripped and the tester is seeing more voltage on the ground than the hot. Be sure to turn suspect breakers off before turning them back on.


Ground should have absolutely no voltage on it. If it does there is a problem.
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.

ronfisherman
Moderator
Moderator
Check wiring in Transfer Switch box.
2004 Gulf Stream Endura 6340 D/A SOLD
2012 Chevy Captiva Toad SOLD

time2roll
Nomad
Nomad
SpaceCoast Fan wrote:
Have you measured the voltage? TV outlet had 13-14 and frigerator outlet had 36.
Need to trace these back to the breaker where I assume you have 120 volts. Check all the connections as a mid wire break is very rare.

SpaceCoast_Fan
Explorer
Explorer
In response to questions:

I did reset all the breakers with no change.

The test is done with utility power or generator power? On generator, No utility power available in storage yard.

Have you found why the tv quit? No power, worked when using power from a different outlet that had normal test reading.

50 amp or 30 amp RV? 30 amp with Onan 4000 generator

Have you measured the voltage? TV outlet had 13-14 and frigerator outlet had 36.

And no I don't believe the Hot & Neutral wires suddenly swapped terminals. I suspect floating neutral of a generator may cause a false reading or you have a bad neutral in a 50a setup.

time2roll
Nomad
Nomad
The test is done with utility power or generator power?

Have you found why the tv quit?

50 amp or 30 amp RV?

Have you measured the voltage?

And no I don't believe the Hot & Neutral wires suddenly swapped terminals. I suspect floating neutral of a generator may cause a false reading or you have a bad neutral in a 50a setup.

enblethen
Nomad
Nomad
I would suggest going into the 120 volt distribution panel. With power off, check all connections, paying special attention to the neutrals (white wires)
I am guessing you have an Onan genset somewhere around 4000 watts.

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker

ndrorder
Explorer
Explorer
Just a big guess that may be the circuit breaker tripped and the tester is seeing more voltage on the ground than the hot. Be sure to turn suspect breakers off before turning them back on.
__________________________________________________
Cliff
2011 Four Winds Chateau 23U