50 amp wiring

jayleona7900
Explorer
Explorer
this may sound dumb but can you wire the neutral and ground to the same ground bar in the electrical box.
10 REPLIES 10

enblethen
Nomad
Nomad
Not always at the electric meter. In facilities where the owner of the facility reads the meter and charges for usage, the neutral and ground are separated.
Connection between the neutral and ground is accomplished only at the service connection point.

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker

wra
Explorer
Explorer
RV electric boxes (the box in the RV) should always be wired as sub panels. In a RV, the ground (green)wire should not be connected to the common (white) wires. There should be bars or bonding points for all white wires in the electric box. The green wire of the AC cable should go directly to the chassis of the RV. Never should the twain meet.
Likewise the box that the RV plugs into is a sub panel. The only place the white and green are bonded is on the MAIN electric box, normally near the electric meter.

Mandalay_Parr
Explorer
Explorer
Not in your RV. Ground and neutral must remain isolated.
Jerry Parr
Full-time
2005 Mandalay 40B
Cat C7 350, 4 Slides
Blue Ox, Brake Buddy
2004 CR-V Toad
jrparr@att.net
602-321-8141
K7OU - Amateur Radio
Kenwood Radios
ARRL, W5YI, & LARC VE
SKYWARN Weather Spotter

enblethen
Nomad
Nomad
Is the "metered panel" the connection point from the utility or is it a sub panel and the meter belongs to the park.

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker

jayleona7900
Explorer
Explorer
this is the metered panel.

jayleona7900
Explorer
Explorer
its wired neutral and ground to same buss bar where the motorhome plugs into.

Golden_HVAC
Explorer
Explorer
The easy way to check your system.

After removing the cover, look where the electricians put the grounds and white wires. If this is the 'meter' panel, then the grounds and white wires will be attached to the same bussbars.

If this is a subpanel, then the white bussbar will be on one side, the ground in another location. You will have several wires going to the panel, 2-3 to the center bussbars and the circuit breakers going out of the panel (or a main circuit breaker) and the white wire to the white bussbar, the ground wire to the grounding bussbar.

Fred.
Money can't buy happiness but somehow it's more comfortable to cry in a

Porsche or Country Coach!



If there's a WILL, I want to be in it!



I havn't been everywhere, but it's on my list.

Kangen.com Alkaline water

Escapees.com

Water-Bug
Explorer
Explorer
wnjj wrote:
Panels that are "downstream" of other panels should have separate ground and neutral. Otherwise if the neutral were to break, the ground would be carrying current which it's not supposed to do.


In other words, neutral and ground are bonded in the main panel and seprerate in all subpanels.

wnjj
Explorer II
Explorer II
Panels that are "downstream" of other panels should have separate ground and neutral. Otherwise if the neutral were to break, the ground would be carrying current which it's not supposed to do.

enblethen
Nomad
Nomad
Are you talking the electrical service panel?
That is the only place that the ground and neutral are tied together.

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker