I'm curious. If one has a 30A RV, but pays for a 50A RV site and then uses a 50A-to-30A adapter on the 50A pedestal receptacle to power their rig ... do they still run the risk of experiencing 30A low voltage service on high usage days?
Of course. It is possible that the 50 amp site might have less voltage drop if the wire size is larger, but you have no way of knowing that till you try both the 30 and 50 sites under load.
I started this thread to point out a significant problem. If the voltage is too low coming into the campground it can only get worse at the connection.
And it usually does get worse.
Typically its going to be wired thus.
![](https://i.imgur.com/6EQpoxxl.jpg)
I doubt anyone is going to go through the expense to run dedicated circuits to each pedestal for 50, 30, and 20, not that it would even matter.
I know of a PA state park that has a 30 amp pedestal between every two sites with 2 30 amp receptacles in each pedestal. The way its wired one recptacle is off the black leg, the other the red, and it alternates that way around the loop. It depends what leg youre on when the place is crowded. One receptacle can be 99 volts while the other is 137 in the same pedestal. I think they have a neutral issue going on.
Instead or replacing the 30+ yr old wiring, or remodeling 5 1960s era shower houses/restrooms, they spent the money upgrading 10 sites to FHU. They're also building a new shower house for their 8 rental cabins, which required about a mile and a half of sewer and water line. Talk about having your priorities in order