MrWizard wrote:
OK. New scenario. Say I just wanted to install a 30 amp plug in a box onto the side of my generator. As long as I use big enough wires, can I just use the following diagram and hook up a new outlet? this way the genny stays the same and I get a new outlet. I know that I will need to run the genny in 240 mode, but I'll only be using 120.
NO don't do it that way, don't run in 220 mode, that will split the windings and give you have POWER/amps on the outlet because you will only be using ONE winding
jumper the wires from the duplex connections to the new RV outlet and leave it in the 120 mode, you will get the full 25 amps.
you can remove the 220 outlet, capp the wires( do not use them ) replace with the RV outlet, and jumper the wires from the duplex to the new outlet
I have a metal bolt on box and receptacle. now when you say jump from the duplex, do you mean( according to the photo) the red wire to one plug. The blue to the other. Then ground to ground. Does this mean that one of the hot wires act as a neutral?