Br and Re go together as (1) pair , ( 1 ) side of the NEW parallel windings
what looks like 'Y' and Bu make the other pair
you need (1) new 30 amp single pole breaker
there is NO neutral bond and NO grounding of the winding,
the breaker can go in line with either pair ( i would use the Br & Red pair as HOT ) and the use the Y & Bu pair as the neutral take your neutral and the HOT from the CB and connect them to your NEW 30 amp RV plug you install in place of the twist lock
remove all the other wiring and out lets
UNLESS you want to put (1) of the old 15 amp breakers in line with (1) of the old duplex to provide an aux connection for power tools
if you do this jumper the new breaker and out let from the 30amp protected circuit at the new RV plug.
any item on that outlet could trip the CB without tripping the 30, but if the combines load was too high you trip the 30 amp CB and not harm/burn of any genny wiring
what looks like 'Y' and Bu make the other pair
you need (1) new 30 amp single pole breaker
there is NO neutral bond and NO grounding of the winding,
the breaker can go in line with either pair ( i would use the Br & Red pair as HOT ) and the use the Y & Bu pair as the neutral take your neutral and the HOT from the CB and connect them to your NEW 30 amp RV plug you install in place of the twist lock
remove all the other wiring and out lets
UNLESS you want to put (1) of the old 15 amp breakers in line with (1) of the old duplex to provide an aux connection for power tools
if you do this jumper the new breaker and out let from the 30amp protected circuit at the new RV plug.
any item on that outlet could trip the CB without tripping the 30, but if the combines load was too high you trip the 30 amp CB and not harm/burn of any genny wiring