MrWizard wrote:
Br and Re go together as (1) pair , ( 1 ) side of the NEW parallel windings
what looks like 'Y' and Bu make the other pair
you need (1) new 30 amp single pole breaker
there is NO neutral bond and NO grounding of the winding,
the breaker can go in line with either pair ( i would use the Br & Red pair as HOT ) and the use the Y & Bu pair as the neutral take your neutral and the HOT from the CB and connect them to your NEW 30 amp RV plug you install in place of the twist lock
remove all the other wiring and out lets
UNLESS you want to put (1) of the old 15 amp breakers in line with (1) of the old duplex to provide an aux connection for power tools
if you do this jumper the new breaker and out let from the 30amp protected circuit at the new RV plug.
any item on that outlet could trip the CB without tripping the 30, but if the combines load was too high you trip the 30 amp CB and not harm/burn of any genny wiring
Thanks mr wizard for your suggestion i will keep it in mind but i have filed a complaint to the BBB about the company and id like to see where that goes before making any "Un-reversible"changes.I actaully tried soemthing similar earlier under the phone supervision of another member here but we were un successful,but we were attempting to use the outlets that are currently available.I did note while i had the panel off that the 2 breakers are 23 amp a piece,kind of an odd number but thats what it says.If anyone can come up with any ideas using current outlets and no cutting of wires id really be interested.
thanks Jason
About Technical Issues
Having RV issues? Connect with others who have been in your shoes.24,210 PostsLatest Activity: Mar 04, 2025