dougrainer wrote:
From your post, it seems you have 2 controls now for the fan motor----The Dino board and the original fan relay which should have been removed when you install a upgraded Fan control module board.
โMar-21-2013 08:38 PM
โMar-21-2013 08:23 PM
gotsmart wrote:
If everything else is good and the consensus is the t-stat, I'll throw this into the mix:
Could it be that the make and model of the t-stat you are using does not perform well in an RV environment?
โMar-21-2013 08:14 PM
dougrainer wrote:
From your post, it seems you have 2 controls now for the fan motor----The Dino board and the original fan relay which should have been removed when you install a upgraded Fan control module board. I don't understand WHY you left the Fan relay in place when you went to the Dino board.
โMar-21-2013 07:49 PM
Old-Biscuit wrote:
You stated "The wiring from the t-stat to the unit is brand new"
You pulled new wire?
Then you have a scape on the insulation that intermittently touches and grounds/shorts.
Blower shutting down at same time burner shuts off is caused by bad/incorrect wiring or faulty relay.
Other than that....I have no idea.
dougrainer wrote:
This is a GOOD example of what happens when someone CHANGES a LOT of parts with NON OEM parts.
dougrainer wrote:
That said, the FIRST place to look is to replace the Time delay (fan relay) on the Furnace. THAT is the gateway to the fan motor. From your post, it seems you have 2 controls now for the fan motor----The Dino board and the original fan relay which should have been removed when you install a upgraded Fan control module board. I don't understand WHY you left the Fan relay in place when you went to the Dino board.
dougrainer wrote:
Also, there is no reason to have to blow out any perceived residual LP in the chamber. The purpose of a sail switch and the delay of 20 to 30 seconds before ignition is to purge the chamber. Doug
HiTech wrote:
What's the 12v system voltage when this is happening? Maybe low? What is the 12v system voltage when it is working fine?
beergardens wrote:
This is my thought too. Suppose your ignitor tip is burned down somewhat and the gap is now too large for the spark to jump across consistently.
โMar-18-2013 12:09 PM
โMar-18-2013 06:45 AM
obscenic wrote:Old-Biscuit wrote:
Then why do you loose programming on t-stat?
At best guess I would say it's getting a shock down the line. .
โMar-18-2013 05:03 AM
โMar-18-2013 04:57 AM
โMar-17-2013 11:44 PM
obscenic wrote:Old-Biscuit wrote:
Then why do you loose programming on t-stat?
At best guess I would say it's getting a shock down the line. The programmable thermostat is removable, it has pin connections to the backing plate which is where the t-stat wires connect. I can take the t-stat off it's backing plate, and leave it sitting on the counter for 3 months and it still displays the time and maintains it's settings.
โMar-17-2013 11:07 PM
Old-Biscuit wrote:
Then why do you loose programming on t-stat?
โMar-17-2013 10:27 PM
obscenic wrote:Old-Biscuit wrote:
Old problem....new board didn't correct.
Yup, exactly.Old-Biscuit wrote:
OK but is the t-stat any good
Brand newOld-Biscuit wrote:
You are losing power at/to t-stat (loosing program/time/date etc.) so either new wiring has a scape on insulation and is grounding out, a loose wire nut, poor connection OR old relay is faulty.
T-stat doesn't get power from wires, it has batteries. There's only two wires going to t-stat; t-stat just opens or closes them to connect 12v back to the furnace.
โMar-17-2013 09:42 PM
Old-Biscuit wrote:
Old problem....new board didn't correct.
Old-Biscuit wrote:
OK but is the t-stat any good
Old-Biscuit wrote:
You are losing power at/to t-stat (loosing program/time/date etc.) so either new wiring has a scape on insulation and is grounding out, a loose wire nut, poor connection OR old relay is faulty.