DD716TED wrote:
Thank you for the response..The one question I have is.. when installing the circuit, do you only connect the AV 115v.. then adjust the switch/potentionmeter to the correct DC Output, then turn off AC ,then connect the battery / dc circuits (fuses), re-energize AC and check that all is working properly..thanks again for your help..
It should come with the mode switch set to three-stage and the pot at 14.6v so you don't need to do anything if that is how you will be leaving it--except you can check the DC voltage is indeed 14.6(ish) before connecting to the battery.
If it is not at 14.6, tweak the pot till it is. Tweaking the pot will change the voltage for all the stages in three-stage mode, so you want to get it started at 14.6 to get 13.6 and 13.2 later when it gets to there.
BTW, there is no 4th stage like with some that do a shot of 14.6 every so often when it is Floating. You have to do that yourself. Real "Equalizing" is done using the single stage mode and set to say 16.2v for wet Trojan batts eg.
Otherwise, you can make sure there is no battery voltage at the DC fuse panel (various ways to do that--eg take the wires off one battery post) and connect the converter wires to the DC fuse panel and measure Dc voltage at the lugs there with meter or from your battery monitor, whatever you have.
Or you could check the DC output voltage with a meter on those wires before putting them on the DC fuse panel.
--------
It should start at 14.6 and stay there about 30 minutes then drop to 13.6. That is too short a time usually.
If you want longer at 14.6, just pull the 120v to it and turn the 120v back on and it will do another 30 minutes, repeat as desired. Or use the single stage mode set to any voltage and it will stay at that till you change the voltage to something else.
I choose to use the single stage mode all the time and leave it at say 14.8v or whatever that is for the temperature the batts are at--eg 14.6 is for 80F but is 15.2 at 35F. So you can do your own temperature compensation.
I leave it at 14.8 till amps taper right down and SG is near 1.300 (wet 6s) and then manually drop it to 13.6. Or with AGMs leave it at 14.4 till amps are down to 0.5a/100AH of battery, then drop to 13.6.
LFP should not be left at 14.x for very long after they are full, so also with them drop to 13.6 for Float time.
That converter with adjustable voltage lets you meet all charging specs for the various types of battery. But you have to do the manual work--it is not fire and forget except in three-stage mode, and that will not meet many battery charging specs as you will know. You could leave it in three-stage if you are always on shore power of course.