MrWizard wrote:
One more test
Check hot #1 to neutral #2
Hot #2 to neutral #1
Make sure those readings are 120v
Or maybe you already did
This will verified they are already connected together
โJun-19-2017 04:47 PM
โJun-19-2017 03:56 PM
MrWizard wrote:
You are good to go
Just make sure that you also use both neutrals, that they get connected together (you did say neutrals, plural)
And the two hots together feeding one 50 amp breaker
Don't want to have just one neutral trying to carry the full return circuit load
โJun-19-2017 10:41 AM
โJun-19-2017 10:28 AM
MrWizard wrote:
sure wish i could get a look at the wiring diagram
IF that is the one i am thinking of you will read ZERO or near ZERO across hot lead leads 1 & 2 going to the (2) breakers
the generator is capable of 120v 54 amps, but you are trying to pull to much from one 30a breaker
IF it measures zero across the hot leads and 120v from each hot to neutral
you should be able to connect the hots to together with (1) 50amp breaker
the problem is me doing something i know how to test for and do correctly
and telling somebody else its OK ?
the hgjab-904 is an emerald microlite belt drive, not the model i'm thinking about
still if its zero volts across the (2) breakers
you should be able to replace with a single 50 and connect them together
as the are already connected internally
and that is key to the whole thing
โJun-18-2017 03:55 PM
MrWizard wrote:
sure wish i could get a look at the wiring diagram
IF that is the one i am thinking of you will read ZERO or near ZERO across hot lead leads 1 & 2 going to the (2) breakers
the generator is capable of 120v 54 amps, but you are trying to pull to much from one 30a breaker
IF it measures zero across the hot leads and 120v from each hot to neutral
you should be able to connect the hots to together with (1) 50amp breaker
the problem is me doing something i know how to test for and do correctly
and telling somebody else its OK ?
the hgjab-904 is an emerald microlite belt drive, not the model i'm thinking about
still if its zero volts across the (2) breakers
you should be able to replace with a single 50 and connect them together
as the are already connected internally
and that is key to the whole thing
โJun-18-2017 03:50 PM
Chris Bryant wrote:
According to the ***Link Removed***, the HJGAB-904 is 120 volt only.
Any way you can separate the other loads while on generator?
โJun-18-2017 03:35 PM
โJun-18-2017 01:49 PM
โJun-18-2017 12:12 PM
โJun-18-2017 12:06 PM
โJun-18-2017 12:00 PM
Chris Bryant wrote:
Unless it is an old unit, or a commercial unit, your Onan is a 120 volt genset, both breakers come off of one single winding. Is your rig a 50 amp or 30 amp rig?
โJun-18-2017 11:57 AM
โJun-18-2017 11:55 AM
MrWizard wrote:
Somebody wired your breaker box wrong? What is the main in your breaker box?
Too much load on one side
It is most likey wired with all your loads on one side including one air
And the other side is only carrying the other air
Yes it could be reconnected for 230v but you don't need too do that
Just need to have a two line input breaker box, using both generator output lines
And balance the load distribution
The other question is the water heater on LP? What about the fridge?
When In hot weather using the genset and air, making sure those stay on LP manually is a good idea, so they don't switch over and use the Onan power
That Onan is big enough provided the loads are balanced