MEXICOWANDERER wrote:
Back when I commuted to work by air (Pterodactyl) I got sucked into recovering new RV "burnouts" so they did not have to be totaled. Proofing a circuit takes time and patience, and comebacks and risk of unintended disaster. I had neither time or patience, wanted no comebacks, nor wished to attend funerals.
I LOADED each circuit to the max. Some with 1,650 watt loads, and multiples thereof to proof incoming feeder lines. Voltmeters, a KW meter on the incoming power, and several fire extinguishers. I used a thermography scanning tool to double check receptacle integrity, breakers, switches, converters, etc. Today a simple IR scan tool the likes of a HF would do fine. As would a pair of electric heaters. Two days to check out a 35' motorhome or trailer. GOOD SAM moaned when I gave them the bill. But they paid and then immediately set me up for the next one. "Jeez I only did this the first time because I knew the guy" he was a golf pro and purchased a lot of batteries off the distributor I subcontracted to. They ended up low-boy'ing rig after rig. Then came a PREVOST. I had to beg off. This occurred not all that far from Los Angeles.
I would park the "repaired" rig far enough away from a dwelling so as to not endanger it. Then use heaters, and a voltmeter and an IR scan tool, and take my time, if I were you.
โSep-19-2013 11:29 AM
โSep-19-2013 11:22 AM
โSep-19-2013 11:19 AM
smkettner wrote:
Wire is protected and may not show any effect.
โSep-19-2013 11:07 AM
tammyinwv wrote:smkettner wrote:tammyinwv wrote:
Since dealer said the first time we got blown appliances the switch was faulty and replaced under warranty but they INSISTED it could not have damaged the appliances.
Time to find a new dealer that has a technition that understands split phase electric service.
That might not help either, as I have an email direct from Progressive Dynamics stating that a transfer switch CAN cause open Neutral. I sent it to dealer, and Anthony at Heartland RV. They then told me that if I had open neutral I would have burnt or melted wires which I did not. So I again contacted progressive, and they said that symptoms of an open neutral could well be ONLY a series of blown appliances which I had. Even with this email direct from the maker of my transfer switch, they still deny warranty. Beleive me, I have that email saved.
Tammy
โSep-19-2013 11:07 AM
smkettner wrote:
Time to find a new dealer that has a technition that understands split phase electric service.
tammyinwv wrote:
The tech did indeed turn off ALL breakers while his voltage/amp (?) meter was plugged into the microwave outlet. The microwave was one of the appliances blown. He would switch on one breaker at a time while checking meter for a change. He also pulled the breaker box out and wiggled the wires behind while checking meter.
tammyinwv wrote:
That might not help either, as I have an email direct from Progressive Dynamics stating that a transfer switch CAN cause open Neutral. I sent it to dealer, and Anthony at Heartland RV. They then told me that if I had open neutral I would have burnt or melted wires which I did not. So I again contacted progressive, and they said that symptoms of an open neutral could well be ONLY a series of blown appliances which I had. Even with this email direct from the maker of my transfer switch, they still deny warranty.
westend wrote:
With the main power turned off, you could pull on the wires attached to the bus and make sure all are tight.
โSep-19-2013 10:52 AM
tammyinwv wrote:I'm loathe to give procedural advice because I don't know anyone's skills and experience. Electricity can be deadly.westend wrote:
I would be getting a second opinion on the problem with a different set of hands and eyes. The #1 suspect would be a loose neutral wire in the load center.
westend could you explain how or if we could check this?
Tammy
โSep-19-2013 10:49 AM
smkettner wrote:tammyinwv wrote:
Since dealer said the first time we got blown appliances the switch was faulty and replaced under warranty but they INSISTED it could not have damaged the appliances.
Time to find a new dealer that has a technition that understands split phase electric service.
โSep-19-2013 10:35 AM
tammyinwv wrote:
Since dealer said the first time we got blown appliances the switch was faulty and replaced under warranty but they INSISTED it could not have damaged the appliances.
โSep-19-2013 10:08 AM
westend wrote:
I would be getting a second opinion on the problem with a different set of hands and eyes. The #1 suspect would be a loose neutral wire in the load center.