Learjet wrote:
For reference the Hartland Contactor in the EMS needs 88 votls to close and will drop out 20-77 volts, according to their website.
So yes, even in by-pass you will still get the contactor to open with extreme low voltages.
http://www.hartland-controls.com/#!blank/c1pqo
ktmrfs wrote:
just the info I was looking for, thanks. So that indicated what I expected, the little honda 2000, doesn't just drop below 104V, it must be dropping down below 70ish volts, which is consistent with sound guys data. However, It only drops down for a fraction of a second, as soon as the relay opens, it pops back up, and relay closes again, then repeat.
Line power will very very seldom exhibit that type of behaviour, the line power is "stiffer", much lower source impedance so if it is dropping down below 70V you are REALLY drawing lots of power, Even a 75A load or so on a 15A branch circuit (what a 1hp motor draws for a few cycles on startup under load) will only drop the voltage down to around 100V, maybe 90 worst case.
However, I suspect the EMS electronics is designed such that it doesn't catch the generator short cycle dropouts AND it can't do anything about the relay chatter with generators, that's a mechancal/electrical function of the relay itself.
โDec-20-2015 08:02 AM
Learjet wrote:
For reference the Hartland Contactor in the EMS needs 88 votls to close and will drop out 20-77 volts, according to their website.
So yes, even in by-pass you will still get the contactor to open with extreme low voltages.
http://www.hartland-controls.com/#!blank/c1pqo
โDec-20-2015 08:00 AM
SoundGuy wrote:
Like you I much prefer the shorter delay of just 15" and would only have use for the longer delay during the summer when we might use the A/C. You're right - waiting for that delay sometimes seems like watching grass grow...
brulaz wrote:
Sheesh, you guys are so impatient.
I've usually got about a million things to do setting up camp outside after plugging in the shore power. So power's always on when those are done, no problem, and I've got the long time delay.
โDec-20-2015 06:45 AM
โDec-20-2015 06:30 AM
SoundGuy wrote:
...
Like you I much prefer the shorter delay of just 15" and would only have use for the longer delay during the summer when we might use the A/C. You're right - waiting for that delay sometimes seems like watching grass grow
...
โDec-20-2015 06:03 AM
ktmrfs wrote:
the ems will wait about 30 seconds (programmable) AFTER it sees 120V to close the contactor to give power to the coach.
SoundGuy wrote:
The OP has a Progressive Industries EMS-HW50C with a user settable delay of either 15" or 2:16 which is set with a jumper on the main circuit board. I've got my own EMS-HW30C currently set with the factory default of 15" for the convenience but once next summer rolls around I'll reset it to 2:16 because the Dometic Brisk II A/C we have doesn't have any built in compressor delay as do some A/C units. It's really annoying as I'd much rather leave the EMS set for a 15" delay but it is what it is and at least the EMS offers me the ability to protect the A/C's compressor whereas without it I can't. ๐
ktmrfs wrote:
I'll bet my 30A unit is also a 15 second delay, just SEEMS like 30 Seconds when your waiting for it to kick in!!!
โDec-19-2015 07:42 PM
SoundGuy wrote:ktmrfs wrote:
the ems will wait about 30 seconds (programmable) AFTER it sees 120V to close the contactor to give power to the coach.
The OP has a Progressive Industries EMS-HW50C with a user settable delay of either 15" or 2:16 which is set with a jumper on the main circuit board. I've got my own EMS-HW30C currently set with the factory default of 15" for the convenience but once next summer rolls around I'll reset it to 2:16 because the Dometic Brisk II A/C we have doesn't have any built in compressor delay as do some A/C units. It's really annoying as I'd much rather leave the EMS set for a 15" delay but it is what it is and at least the EMS offers me the ability to protect the A/C's compressor whereas without it I can't. ๐
โDec-19-2015 01:46 PM
โDec-19-2015 08:36 AM
ktmrfs wrote:
the ems will wait about 30 seconds (programmable) AFTER it sees 120V to close the contactor to give power to the coach.
โDec-19-2015 07:36 AM
BillyandKris wrote:
Thanks to all for the input. It has given him an idea of something else to check. The power has and is at constant 118-122 V @61 H. Never showed error code and power never disconnected or dropped. The ATS was silent. Sound came from the Progressive EMS and you could put your hand on it and feel it. After reading your inputs and thinking back he says that just a few days before they had replaced the 30 amp breaker on the big generator. Now he wonders if the 50 amp breaker is getting weak. He (being Hubby) says breakers are not meant to be turned off and on constantly and these are turned off and on a lot because we have to check the generator fluid levels almost daily--we turn the breakers off before killing gen--after cranking the gen back up we turn the breakers back on so the gen does not crank up under a full load. Hmm we always turn everything off in the camper so maybe we should stop turning the breakers off since we are not really cranking the gen up under a full load!! BTW we have 50 amp in our camper. The sound has never returned. We may need to get our service guy to replace the 50 amp breaker at the generator. Think we will put our pantry back together and wait and see. Will check on contacts replacement. Maybe we should just bypass the EMS since we really don't need it here with our constant power source. We are totally running on the big generator; no shore power here.
โDec-19-2015 01:26 AM
ktmrfs wrote:
And you mentioned your experience with the honda generator. In my case my unit has the bypass switch. turning the switch to the bypass position with the generator has no effect on the chatter, it chatters in either case, so even if you had the switch it wouldn't have solved the problem.
โDec-19-2015 01:07 AM
BillyandKris wrote:
Maybe we should just bypass the EMS since we really don't need it here with our constant power source. We are totally running on the big generator; no shore power here.