Atwood 15K Rooftop Heat Pump Md #15028

I recently purchased a 15K Atwood Air Command Heat Pump Model 15028; it’s a ducted unit with a digital thermostat. The Original unit was a Dometic 13.5K AC. The removal of the Dometic and install of the Atwood was a breeze, the hookups are about as simple as it can get. The only problem is that it won’t work in heating mode; The AC works great, no problem. I thought it was a faulty thermostat so i purchased another, no luck, it will come on and output excellent heat for about 20 seconds when it wants to, no rhyme or reason just whenever it feels like it, most of the time it wants to run the propane furnace, the reason I purchased the heat pump was to get away from the expense of propane and the clutter of having three cube heaters on the floor. After scouring the net for troubleshooting info I've found that every other RV heat pump I've researched is wired the same as most standard residential pumps, with separate wires calling for whatever function. With this Atwood unit, OH No. It's a four wire deal that uses pulses or some******that makes no sense to me and won’t show change on a multimeter. Had I done more research as to how the controls were built I would not have bought the damn thing. The rest of the unit design appears solid. At this time it's only 48 degrees outside so there is no excuse for it not to be running. I have spent a couple of weeks fooling around with this pc of garbage. Had they simply used a traditional control board, I’d be up and running with whatever thermostat I chose instead of some space **** they probably had aboard challenger. I just don’t get it, why would you go from using a controller that’s tried and true, used in millions of systems, to some space trash. I sure would appreciate any feedback anyone could give me about their heat pumps. Especially Atwood.
  • 1. Atwood is the new kid on the block. So, you will be hard pressed to find knowledgeable help.
    2. Ambient sensing is critical to RV HP operation. IF the ambient sensor senses incorrectly, it will default to Furnace.
    3. Disconnecting the furnace will not help troubleshooting, it just makes sure you will not have the furnace running while you do troubleshoot.
    4. Have you tried Atwood for help?
    5. The Tstat is the Atwood tstat correct? Doug
  • Yeah, I have the furnace disconnected right now. I have my multimeter on it so I can hear when it calls for heat, earlier today when the sun was up and it was getting a bit to warm in here to stand heat the damn thing worked great. I don't need heat when it's hot in here AAaaaarrrggghhh.. So I turned on the AC. Worked like a champ.. I just don't get it. HP=AC Reversed,, If only it had standard inputs, I could trick it into running until I can get out and get to a Atwood Tech. I'm off the road a bit and it will take a while for the yard & driveway to handle my weight, It's still pretty soggy up here in VA.
  • Some manufacturers do that push thing for the setting and constantly display the room temp but what you describe sounds like a bad thermostat. China is about as good making thermostats as they are at making dog food. Have you tried disconecting the furnace wire to see if the HP will continue to run without that circuit? Or was that what you were talking about in your post? Some type of digital control?

    If that control is digital, there is a good possibility that somthing like floresent lighting could be messing with it.
  • Yes, I have taken that into consideration and only moved it in 1 degree increments every ten mins, most times it wont come on at all. In order to see what it thinks is room temp you have to push the sleep button for 5 secs, I can push it and it may tell me its 72, I can pu**** again it may tell me its 80, push again it might be 76, mind you this is in a 20 second span. Why the hell should I have to push it at all to see what it thinks the room temp is, as opposed to the set temp? what engineer came up with that?
  • If it operates like my Coleman,when you set the thermostat more than 5 degrees above the space temperature it will automatically revert to LP. Have you tried setting the temperature 2 or 3 degrees above the room temp?