Internal of some GFCI receptacles for feed through function is separate from the GFCI circuit.
Plugging in a three light tester would show, open hot, open neutral, open ground.
This is on my Ames GST-125. Mes GST-125
Tester would be plugged into dead receptacle(s).
It won't tell where the problem is. Only guaranteed test of GFCI feed through feature is with voltmeter connected to load terminals.
Plugging in a three light tester would show, open hot, open neutral, open ground.
This is on my Ames GST-125. Mes GST-125
Tester would be plugged into dead receptacle(s).
It won't tell where the problem is. Only guaranteed test of GFCI feed through feature is with voltmeter connected to load terminals.