Will the rear one work on shore power with the front one off. If so I'd say it's the power management system. As it will let both run when on generator power. It may also be that of the 2 breakers on the generator one may be just for the rear air. Turn the generator breakers off one at a time and see if the rear air goes off.
Just make sure you wait a few min.s before you reset the breaker if the AC is still on it needs time to bleed off the head pressure.
Just make sure you wait a few min.s before you reset the breaker if the AC is still on it needs time to bleed off the head pressure.