Atwood/Dometic Stove regulator 51062

I have a Atwood range model R-A2133BSE. I am having issues with the stove regulator to sustain 10" WC and I need a sanity check if I am missing something.

Background. Earlier this week, I did a LP leak test and pressure test on my camper. I am using my new Dwyer gas gage.

I hook up the gage at the burner orifice, read the pressure. I am getting 10" WC with a tap on the gage at the burner orifice downstream of the stove regulator. OK this sounds good. I close the main tank valve.

I vent a burner to bleed down to 8" WC at a burner orifice to open the main tank regulator. I let the system sit for a 3 minute leak test, no drop. I let it continue to time for 10 minutes. No pressure drop. Great, I have no leaks.

I then take the gas line off "upstream" of the stove regulator to do a system pressure test. Hook up the gage, open the tank and I get 10" WC. OK what's up? I then suspect my gage is not reading right. I go get my old water manometer. Sure enough it is reading right on with the gage. OK the tank regulator is acting up.

I adjust the tank regulator up to 11 1/2" WC before the stove regulator. Fire off the furnace and the system drops down to 10" WC. I never had much luck trying to adjust these cheap tank regulators, when they start acting up, they are usually toast.

But, I tweaked the regulator up to 13" and with the furnace running it drops to about 11 1/2". Now let me check the stove regulator again as I really do not know if it was working right.

I put the incoming line back on the stove regulator, and put the gage on the burner orifice and check the pressure at the stove burner. Yup, it reads 13"WC. Darn, the stove regulator is bad too.

I order a 3 new tank regulators and 3 new stove regulators as I have several campers. They are all over 10 years old. And all using Atwood ranges.

Today I put the new tank regulator in. That works right now. When the furnace and water heater are on, it only goes from 12" WC to 11" WC. SO I feel good the tank regulator is good now.

I put a brand new Dometic 51062 regulator in the stove. Take a reading at the burner. I get 12" WC. This new regulator is not working. I check it again with my manometer, same thing, 12" WC.

Ok, so I go get a 2nd new Dometic 51062 and put it in. Same thing. It passes full tank pressure at 12" WC.

OK what am I missing here? I have had stove regulators go bad in the past when Atwood was still in operation and the new replacement worked right out of the gate. It was 10" WC right on the money. (now about 8 years ago) Now I have 2 new Dometic ones since the takeover of Atwood and neither one works.

I have not yet opened the 3rd spare stove regulator. I even tried putting the regulator face up (diaphragm axis up) verses 90 degrees like the stove was originally. No luck

Any suggestions?'

This I will say, the older Atwood regulators you could pull the plug out and adjust the pressure. These new Dometics are sealed up with what looks like a pressed in disk over the diaphragm stem, so it is non adjustable.

Thanks in advance.