It sounds like your furnace control board is sensing a DC voltage from your converter (charger) that it considers too high. In other words, it won't start until it no longer senses charging voltage, but waits for the lower battery voltage.
Have you tried starting the furnace, then turning on the generator? Will this cause the furnace to shut down?
Have you tried starting the furnace, then turning on the generator? Will this cause the furnace to shut down?