hbski wrote:
Chris Bryant wrote:
Rather than spend a couple of thousand on an inverter setup, I would spend a couple of hundred to properly quiet the Onan.
That said- the new Xantrex Freedom SW series will do generator support as well, and power share down to 5 amps.
As I understand it the Xantrex does not sync with the incoming AC and thus doesn't do true support, but rather switches to inverter only when you exceed the AC input and then switches back after the load reduces
You may be correct- I'm not 100% certain, but the new model states:
Xantrex wrote:
GEN Support allows power to be automatically drawn from the batteries to
assist an AC generator to support heavy loads (i.e., loads that exceed the
available current from the generator).
Generators have a limited output current and it is possible to reach this limit
when operating heavy loads. The Freedom SW is designed to assist the
generator when heavy current demands load down the generator by
supplying additional power from the batteries.
In addition, the battery charger can reduce its charging current to the
batteries so the combined charge AC current and total load current does not
exceed the capacity of the generator or trip its output breakers or fuses.
I know they also will stack either in parallel or series for double current or 240 volt operation.