Why no Honda EU2000i Parallel In Canada?
Just got a clarification why the certain Canada-model Honda EU-series generators do NOT have parallel connections. (Exception: the EU1000i does).
The (Canada) CSA rules don't say "no parallel" but what they DO say is 'no power allowed that exceeds the capacity of the receptacle/breaker.'
So, in the case of the standard EU2000i, it has a 20A duplex receptacle, and puts out 13.3 amps. There's also a 20A breaker on the duplex (only). So far, so good.
However, if you connect another EU2000i in parallel, the 20A breaker is NOT part of that parallel connection circuit, AND the combined amperage of the two units is now 26.6A, which exceeds to 20A rating of the receptacle. Verdict: No parallel connection for you on this model.
In the case of the EU2000i Companion, with its 30A receptacle, Honda probably could offer it with parallel, but it would not work with standard EU2000i that does not have parallel connectors. This would require a Canada customer to buy 2x Companions to get parallel, and at least in US $, that would be a $250 premium. Probably would NOT be a good seller.
In the case of the EU1000i, it has a 15A receptacle, and creates 7.5A. It also has an internal 20A circuit protector (no external breaker). When combined in parallel with another EU1000i, the total currrent is 15A, which is okay by CSA, especially since there is a 20A protector circuit. So, the EU1000i in Canada *does* come with parallel connectors.
For the rest of the EU-series models (EU3000is, EU3000i Handi), they are in the same boat as the EU2000i; too much power is possible through a too-small-rated receptacle when connected in parallel, so no parallel connections allowed.
Finally, it's my understanding some other brands of generators sold in Canada do offer parallel connections, but I don't know which ones. Evidently, they have the legal-sized receptacles and/or breakers/protectors that do meet CSA rules.
Hope this clears it up for those who asked.
-Robert@Honda
Caveat: I work for Honda, but the preceding is my opinion alone.
The (Canada) CSA rules don't say "no parallel" but what they DO say is 'no power allowed that exceeds the capacity of the receptacle/breaker.'
So, in the case of the standard EU2000i, it has a 20A duplex receptacle, and puts out 13.3 amps. There's also a 20A breaker on the duplex (only). So far, so good.
However, if you connect another EU2000i in parallel, the 20A breaker is NOT part of that parallel connection circuit, AND the combined amperage of the two units is now 26.6A, which exceeds to 20A rating of the receptacle. Verdict: No parallel connection for you on this model.
In the case of the EU2000i Companion, with its 30A receptacle, Honda probably could offer it with parallel, but it would not work with standard EU2000i that does not have parallel connectors. This would require a Canada customer to buy 2x Companions to get parallel, and at least in US $, that would be a $250 premium. Probably would NOT be a good seller.
In the case of the EU1000i, it has a 15A receptacle, and creates 7.5A. It also has an internal 20A circuit protector (no external breaker). When combined in parallel with another EU1000i, the total currrent is 15A, which is okay by CSA, especially since there is a 20A protector circuit. So, the EU1000i in Canada *does* come with parallel connectors.
For the rest of the EU-series models (EU3000is, EU3000i Handi), they are in the same boat as the EU2000i; too much power is possible through a too-small-rated receptacle when connected in parallel, so no parallel connections allowed.
Finally, it's my understanding some other brands of generators sold in Canada do offer parallel connections, but I don't know which ones. Evidently, they have the legal-sized receptacles and/or breakers/protectors that do meet CSA rules.
Hope this clears it up for those who asked.
-Robert@Honda