Forum Discussion

kg1d_dx's avatar
kg1d_dx
Explorer
Jun 16, 2018

Power Problum

I made up an extension cord for my rv. It is a 50 amp system, the problem is when I put power to it one leg is 115 volts and the other is 150 volts. At the outlet the voltages are 115 each leg, plug in the extension cord and at the far end its 115 1nd 150 volts, I changed out the hot wire on the 150 volt leg but still no change. Any Ideas whats going on?
  • Check the neutral wire connections over carefully. It may be open and the voltages you're measuring with the high-impedance multimeter are a result of it floating to more or less arbitrary voltages. If the neutral is open, the individual leg voltages may be wrong but the voltage hot to hot should be steady and correct at a nominal 240 volts...or, in rare instances, 208 volts if it's two legs of a three phase Y supply.

    Obviously, don't use the extension cord until you get it sorted out properly. An open or high-resistance neutral can cause all sorts of damage to things plugged into the circuit as the voltage fluctuates rather wildly.
  • You have a bad neutral. It could be a bad connection at either end of your cable, or a break in the cable. Check the voltage between the two hot legs, it should be very close to 240 volts. You cannot rely on adding your readings from each leg together. When the neutral is compromised, voltage on each leg will fluctuate wildly whenever any load is introduced, including your voltage tester.
  • Check your connections. I would be willing to bet you have a cat whisker jumping between two terminals.