Electrical Myth

While searching through the forums recently, I came across two posts in which an old electrical myth is repeated- "Circuit breakers will trip at 80% of their rating." For any breaker which has not degraded from age or other reasons this is absolutely FALSE! A breaker will trip according to its trip curve which is published by the manufacturer. The following link is to a pdf from Square D for their type QO breakers, a very common type. Curves are published by every manufacturer for every type of breaker. You will notice that the curves are vertical exactly at the 100% mark. At any value of current to the left of the curve (< 100%), the breaker will not trip.

http://static.schneider-electric.us/docs/Circuit%20Protection/Miniature%20Circuit%20Breakers/QO-QOB%20Circuit%20Breakers/0730CT9801R108.pdf

This misconception has been repeated for generations due to NEC rules for certain types of circuits for which the load is limited to 80% of the circuit rating. This is a safety factor, nothing more. Nowhere in the NEC is it stated that a breaker will trip at 80%.
Now, let the debate begin, but look at those trip curves first. I'll wager that 99.9% of you have never seen one.