Voltage drop from solar controller

or: Here we Go Again.

Still trying to get my 420 Watts of solar to fully charge my 484 AH of battery. (Currently in southern Mexico.)

Layout:

2 80 Watt panels and 2 130 Watt panels in parallel, 420 Watts (Went parallel rather than series because where I park one or more panels are soon shaded.)


4 6 volt GCs rated at 242 AH each, total 484AH

Controller: Bluesky Solar Boost 2000E MPPT Controller. Bluesky is a two stage charger. Bulk charge voltage was set at 14.4 volts, op from default of 14.0 RECENTLY increased to 14.67V

Also charge via Xantrex Prosine 2.0 PSW inverter charger. Bulk Charge set to max at 14.4 volts.

The output voltage from the controller would always read higher than the battery voltage as reported on the Xantrex remote. (Accurate)

From Controller output about 8 feet of #10 fused with 30A fuse
THEN approximately 20 feet of I think #6 to batteries.

At the junction of the fuse the wire connects to what was originally the connection point for the converter DC Output and also feeds the 12V breakers for the 12V systems. This connection point is 20 feet or more from the batteries. It is impossible for me (physically) to follow this cable end to end. (The converter is no longer there.)

Before I increased the controller output voltage from 14.4, when the controller read 14.4 as the battery voltage then begin reducing current. The battery voltage as displayed by the Xantrex remote would only be 13.7, the same as measured by DVM at the batteries. 0.7 volts drop.

Of course the batteries never reached 14.4V. As the day progressed and the panels became shaded the charge current eventually dropped enough that the controller would pass all available current to the batteries, whose voltage might reach 13.8V.

A couple of days ago I increased the Controller output voltage to 14.67 (the control is touchy). Batteries still have not reached more than 13.7 Volts when the controller was passing maximum current (19.0 Amps) before noon. Controller at 14.67, batteries at 13.7! a full volt drop! Increasing the Controller voltage gained nothing apparently.

NOW: 6:20PM Sun gone, no solar input, minimal 12V draw, Controller reading batteries as 12.76V, the Xantrex says 12.8

Enabled Xantrex charger (max charge set at 96Amps) Starts charging at 62 A, 14.2 Volts, charge rate decreasing as I watch, within a minute or so it settles down at 28 Amps, batts still at 14.2V. I expect both will slowly decrease.

CONCERN: I checked the fuse holder temperature with my ir gun: 108F. Quite warm to the touch. The plastic body of the fuse itself and wires registered 83F, ambient on the floor was 81 or 82. This is the same (rather replacement) fuse holder that melted last year.

QUESTION: I have a spare fuse holder, what appears to be a higher quality one, from AutoZone. Should I replace it?

Question: How fully are my batteries getting charged from the solar? I have been in the habit of enabling the charger on cloudy days or at least once a week.

MY CONCLUSION

I really need to beef up the cables from the output of the controller to the batteries. Will I be wasting my time going up one size to #4 or should I bite the bullet and see if #2 or even 1/0 will fit?

OR third QUESTION: Do I need to replace the controller with one that I can put in the elec. compartment near the inverter, about three or 4 feet from the batteries?

NOTE to the curious: Yes I could run the charger 24/7 but here in Mexico electric power is VERY expensive. I have the panels, so why not try to save the CG owner, a friend, a few pesos here and there.