MrWizard wrote:
yes i'm in SoCal
i'm sure the generator is running near max
but at these temps the A/Cs are hot and pulling full power
the Onan gets hot and gets to point where it is difficult for it to do compressor restarts
put the A/C's on auto, select a low enough temp on the stat, that the A/C comes on and stays on, does not cycle the compressors
makes it a bit cool in the morning, but that helps combat the heat penetration
ran the generator and one A/C all night last night, right now 105 here
Jul-07-2018 11:37 AM
Jul-07-2018 11:21 AM
time2roll wrote:
(copied from link below): Section 210.20(A) of the code basically says that a circuit breaker for a branch circuit must be rated such that it can handle the noncontinuous load plus 125% of the continuous load. (A continous load is one where the maximum current is expected to continue for 3 hours or more.) In other words, the breaker needs an extra 25% capacity of the continuous load for headroom. That, of course, means you need a larger, more expensive breaker.
https://blog.schneider-electric.com/datacenter/power-and-cooling/2014/06/12/clearing-confusion-80-vs...
No one actually applies this rule as it is not required for an RV because all items are short term or thermostatically controlled so by definition an RV is not a continuous load. However as you have experienced it is easy to have the air conditioners run continuous for 10+ hours and the EMS will hold the RV very close to 30 amps for well over the 3 hour requirement. Then you have the booster that will draw more amps to get the voltage corrected.
IMO this can put you in the continuous service definition. Ever wonder why so many 30 amp connectors and adapters are burn, worn, and heat damaged? OK not just this but I believe it contributes significantly.
This is part of the reason I suggested all breakers off if running 2x A/Cs. Yes you will be running on battery power for the 12 volt systems while the 120 volt system is under stress. That last 4 amps can make a difference. Turn the rest back on an hour or so after sunset when the system is less stressed. Otherwise make do with one A/C or find 50 amp power.
JMHO
Jul-07-2018 11:15 AM
MrWizard wrote:
I bought this Bounder 36S, last Sept, moved from the DP to the Bounder in Dec
I have not yet plugged in anywhere
Strickly on generator and Add on inverter
This RV has 30 amp shore cord
I have the intellitec load control also
The rear A/C is on a breaker in the panel
It appears the front A/C is on the 20 amp circuit breaker of the Onan 5000 and goes thru the inteltec but not thru the breaker panel
No breaker in the panel turns the front A/C off
Because it was 116F yesterday, and 95F at 2am this morning
The generator has been on for 26 hours, since Friday morning 7am
Today the prediction is 111F
Jul-07-2018 10:56 AM
wa8yxm wrote:
30 amps you are doing well if you can run both A/C.
If you are seeing that much voltage drop between your Surge Guard and your INdoor Voltmeter.. Let me make an assumption
Park---Hughes autoformer---Surge guard---RV
IF that is how you are set up then do the following
First with the RV not plugged into the surge guard compare the surge voltage reading to the volt meter's reading. You may find a difference. if so you need to figure out which one is right.. Though I DO know how to calibrate a volt meter or check calibration.. Too detailed to describe here. Plus you need a calibrated source I have one but.. Well.
Now if the meters agree Take a look at your power plug. are the blades Bright and shiny or black as knight? (this is mostly the 30 amp plug) Not so much 50s) Dirty/tarnished plugs drop voltage. they also tend to MELT at full power load.
But that is way too much loss between Surge Guard and inside outlet.
Jul-07-2018 10:54 AM
Jul-07-2018 09:43 AM
pianotuna wrote:
A 30 amp service should only be used at 24 continuous.
If the autoformer is raising the voltage 10%, then on the input side of the autoformer the current would be much higher than 29 amps.
Anything above 107 volts is safe for the air conditioners. How are you checking the voltage inside the RV?
Jul-07-2018 08:53 AM
Jul-07-2018 08:11 AM
Jul-07-2018 07:25 AM
cm2785 wrote:
...I accidentally turned my new AC off yesterday and turned it back on about 15 seconds later and the compressor seemed to struggle so it went back to fan mode and about 20 seconds later it kicked back in just fine...
Jul-07-2018 06:58 AM
Jul-07-2018 06:47 AM
Jul-07-2018 06:39 AM
pianotuna wrote:
Does the Intelligec do "load shedding"? If so, go ahead and use both air conditioners, but DO monitor the voltage and manually shut down one air conditioner if voltage sags below 107.
Does the Intelligec allow you to preset incoming amps? I do this using my Magnum hybrid inverter charger, so on a 15 amp shore power I "dial it down" to 12 amps. On 30 amps shore power, I dial to 24 amps, and on 50 amp shore power, I dial to 30 amps.
If there is a 50 amp outlet, get a 50 to 30 adapter and use that for the shore power. Since a 50 amp can be run flat out at 40 amps, that leaves more for your RV to work with, and voltage drop may be less (I still often use my autoformer).
Jul-07-2018 06:32 AM
rgatijnet1 wrote:
There are several things happening that you do not show with your meter readings. What you do not show is the increase in amperage, and voltage drop, when one of your AC units is first starting the compressor. This can add several more amps as well as drop the voltage 2-5 volts for a short period of time until the compressor is up and running.
Another things is that as the voltage drops, your amps used will increase for all electrical items in your coach.
If you hear your AC compressors struggling to come on, that is the best indication that the voltage is too low. This is especially true if the AC compressor cannot get started and drops back in to a fan only mode.
Volt meters are fine but they only give you an instantaneous voltage reading on a power supply that is constantly changing.