Aqua Hot

sansouci2
Explorer
Explorer
I have a 2003 Monaco Exec 40 ft. The Aqua hot was not warming the living area or the bathroom, the bedroom was toasty warm. Took it in and they found one leaking pump out of 3 pumps. They replaced it and put antifreeze( about 8 gallons)back in. The aqua hot fires up and gets hot, problem is the living area and bathroom are still cold. any ideas what is going on????
36 REPLIES 36

sansouci2
Explorer
Explorer
They still have the MH. They actually replaced the leaking pump, not the valve. I am just trying to figure things out too. We really want to head south soon!

gutfelt
Explorer
Explorer
sansouci2 wrote:
Thanks for the advice so far! The RV shop has done both these things. The Aqua Hot Tech seems to think there is a air lock somewhere in the system. Any ideas?


Ok in your first post you never mentioned they replaced the valve hence my remark >> It very well could be assuming your sure the valve is functioning and the pump is running that only leaves one option "air lock" but why would a repair shop give you back your MH when they obviously never fixed the problem?? seems odd to me
DOES the "Fan" come on in the zone that's not heating??????

sansouci2
Explorer
Explorer
Thanks for the advice so far! The RV shop has done both these things. The Aqua Hot Tech seems to think there is a air lock somewhere in the system. Any ideas?

gutfelt
Explorer
Explorer
Mr.Mark wrote:
Also, there is a reset button on the Aqua Hot itself that you have to use the end of a paper clip to reset.

Good luck, Aqua Hots are great heaters!
MM.


the reset has nothing to do with one zone not heating; the reset button controls the entire unit operation

gutfelt
Explorer
Explorer
sansouci2 wrote:
I have a 2003 Monaco Exec 40 ft. The Aqua hot was not warming the living area or the bathroom, the bedroom was toasty warm. Took it in and they found one leaking pump out of 3 pumps. They replaced it and put antifreeze( about 8 gallons)back in. The aqua hot fires up and gets hot, problem is the living area and bathroom are still cold. any ideas what is going on????

you had a idiot work on it is what happened. The one way boiler fluid valves that control heat to each zones stick. all you have to do is tap on it and they usually start to work or if worried of it repeating install a new one; I usually run mine in the early fall late summer just to make sure there working; I had one do this about 5 years ago and its never stuck since

Mr_Mark1
Explorer
Explorer
Also, there is a reset button on the Aqua Hot itself that you have to use the end of a paper clip to reset.

Good luck, Aqua Hots are great heaters!
MM.
Mr.Mark
2021.5 Pleasure Way Plateau FL Class-B on the Sprinter Chassis
2018 Mini Cooper Hardtop Coupe, 2 dr., 6-speed manual
(SOLD) 2015 Prevost Liberty Coach, 45 ft, 500 hp Volvo
(SOLD) 2008 Monaco Dynasty, 42 ft, 425 hp Cummins

Ivylog
Explorer III
Explorer III
There are check valves above the pumps that are know to stick closed. Tapping on them with the wooden handle of a hammer should unseat them. Anyone who works on AH should know this.