mchero wrote:
Something else to throw in the mix folks.
Should their be a 300Amp fuse between the inverter & positive post?
I have zero gauge between the positive inverter post and the batteries BUT that &^#$ fuse heats up! Not hot enough to burn but hot. Not sure what I'm loosing thru it. Ideas?
โNov-11-2015 05:56 PM
โNov-11-2015 04:29 PM
โNov-11-2015 02:33 PM
โNov-11-2015 02:29 PM
Supereri73 wrote:
I think this shows your last suggestion. Please let me know if I still don't have this.
Thanks to everyone for all the GREAT feedback on this!!!!!!!
โNov-11-2015 12:41 PM
โNov-11-2015 12:40 PM
smkettner wrote:
1/0 ampacity is at least 250 amps so yes it will work fine at 100 amps.
Keep it short and neat for best results.
http://www.genuinedealz.com/voltage-drop-calculator
The side to side run will cause some voltage drop and should be added to the inverter cable length calculation. Probably better overall to get all batteries in one compartment near where the inverter will be installed. Far better to lengthen the wire to the house loads and keep the inverter connection short.
โNov-11-2015 12:26 PM
DrewE wrote:
Basically, you need either the positive or the negative connection to the battery bank to be at the far side, and the other one to be at the near side, and only one of each. You can achieve that in a few ways: by using a long wire to connect the far side ground connection to the current near side ground (via the shunt), by using a long wire to connect the far side positive to the near side positive stuff, or by making the ground connection for the batteries at the far side (via the shunt). It seems to me the last option is the simplest, and requires only lengthening the sense wires to the shunt and finding or making a good ground connection on the far side.
โNov-11-2015 11:43 AM
โNov-11-2015 11:24 AM
Supereri73 wrote:
Would 1/0 be big enough for say 100 amp load?
โNov-11-2015 10:51 AM
โNov-11-2015 09:31 AM
Supereri73 wrote:
I can run a second ground from the far side and use that for the Shunt/Load- . Running the cable will be easy.
Would 1/0 be big enough for say 100 amp load?