The inverter does have a ground to neutral relay which connects ground and neutral during "inverting" mode and disconnects ground and neutral when transferring to shore power.This neutral to ground relay is required by UL458 which is the listing for ...
Paul127,It sounds like when you have the inverter "ON" you have 120v power in the coach but if the inverter is "OFF" no power on the output side of the inverter and NO charging.The next thing to check is with a ac volt meter you should have 120v at t...
Yep so what you have is a newer remote on an older AGS module. The newer remote feature of RV/Other works because it is all programmed in the remote itself. It says "no comm" from the AGS module because the older AGS module cannot talk back to the re...
Are you sure you have an ME-AGS-N? The -N didn't come out until 2008. The original ME-AGS has 5 knobs for adjustments and all the settings are done from there not in the remote. The -N does not have any knobs as all the adjustments are made from the ...
If it is just the display on the remote, unplug the remote from either the remote or at the inverter. Wait a minute and plug back in probably will fix the issue. The plug is a standard phone jack and usually easiest to access at the inverter in the b...