Received my parts Thursday and installed them Friday. Like most everything that appears to be simple there is always a twist that makes it more difficult. The wires were burned badly so I was having a little difficulty identifying them. The schematic shows the heat pump reverser valve connected to the HERM circuit (start winding). Did not think that was correct so I thought I would take a look at the other AC unit. This unit has been acting kind of goofy. Just before it turns off you can hear the fan speed increase. When I opened the electrical junction box in the upper unit I found out why, the same capacitor had come apart and the OPTCR fell apart in my hand. I am assuming it performed enough for the compressor to start but leaked enough current it affected the fan speed. I have noticed in the past circuit the AC circuit breakers would trip for no apparent reason. I guess there was a reason. So for a while I had no AC, got the bedroom up and running and then called around and found a generic capacitor with an OPTCR on it. Installed it in the front unit and now we have two AC units again.
Next time I notice goofy fan speeds or circuit breakers tripping for no apparent reason, I will check these capacitors.
P.S. When the compressors first turn on the total current draw is nominally about 11 amps. After a few minutes (I assume compressor head pressure increasing) it settles out at nominally 15 amps. I assume this is normal?
More lessons learned, now if I could just remember them, what were we talking about?
2006 Monaco Diplomat