Bank These Batteries? UPDATE

BFL13
Explorer II
Explorer II
Updated 28 April

(Changed topic so starting new thread)

Now I need an opinion/facts if I can bank this big one with my two smaller AGMs even though they have different "cycle use" charging specs (lower 14s vs higher 14s) They do have the same Floating specs.

If I did, then I would be running inverter loads on the 450AH bank too. Now I use the two 100s for inverter and the 250 separately for the rest of the 12v stuff.

A. Just bank them and discharge and recharge them all at once
B. Bank them only for discharge and recharge separately
C. Leave them separate the way they are now (means usually getting the big one down to 50% while there is still lots left in the inverter's bank)

This big AGM seems to have been built at or next door by the same factory as my two 100AH AGMs. They even have exactly the same carrying handles. Their spec sheets/graphs are written to the same format.

Here are the two spec links again--

EDIT--had the the wrong link for the big one, sorry! Mine is the ESG with 14.1 to 14.4 for cycle use, but the other link has the same other specs. (it would be too easy if these two 6GFMs were in fact the same battery and had the 14.8--)

http://www.esg100.com/index.php/product/index/g/e/id/35.html

http://www.wegosolar.com/products.php?product=SKR%252d125AGM-Stark-AGM-12V-Solar-Battery-Sealed-125A

http://cn.yahengpower.com/data/upload/file/201612/8b4d4c59da39f4428b9ff79f380ab271.pdf

BTW, bestconverters is selling that "Stark" one (mine are actually 121 100AH but wegosolar has now gone to the 125 version--same specs) as a "UPG" brand. (They seems to all come from that same factory in Canton ๐Ÿ™‚ )

http://www.bestconverter.com/UB121000-100-AH-Deep-Cycle-_p_293.html#.WuJQYlKWxLM
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.
14 REPLIES 14

BFL13
Explorer II
Explorer II
MEXICOWANDERER wrote:
With AGM there should be near zero transfer. .15 volt difference is excessive. The high will be feeding the low to balance. When is operational stasis if that much potential is evident, grab your DMM set it for 10-amps and then find out how many milliamps are draining. Check it again an hour later. Imbalance still there?
what this "proves" is differences in chemistry. The closer the batteries pencil out the batter they will get along during the charge and discharge cycles as well as float.


The test as far as it went says they are at 0.01 volt difference. I am going ahead with banking them, based on what people have said in this thread wrt any risk, and to get some advantages in the MH set-up doing it that way. ( I couldn't do it before with the old and tired Wet 6s in there instead)

After several trips off grid in this MH learning as we go, it is more clear what we need and don't need in the way of a set-up for power use. (Same thing happened with the 5er we had. Each trip you see something else you could do to make things better.)
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

BFL13
Explorer II
Explorer II
Well I screwed that up, but maybe still get the answer, depending on what Mex says.

Turns out I only had two batteries banked. I missed a connection with Stark 2 back under the sink. Didn't notice this morning because all the batts were near same voltage.

So I took 220AH from the 350AH bank I did have (by temp at 333AH, so I am down to about 34% on the 6G and Stark 1, while Stark 2 is still full.

On disconnecting the bank and a couple minutes for bounce back, voltages are: 6G--12.10, Stark 1--12.12

EDIT: After an hour of bounce back 6g--12.16, Stark 1--12.17
EDIT 2--After 2 1/4 hrs 6G --12.16, Stark 1--12.17 no change in last hour.

--------------------------
SO-- now recharging. Can't stand leaving them that low and they are close in voltage now, so I ASSume they will be close in voltage tomorrow. Mex can comment if any of this proves anything at all.
---------------------------

The vague voltage/SOC graph says 34% should be about 12.2 so that works. Now I am supposed to wait till tomorrow afternoon to recharge them. ( I don't like to leave them at 34% like that. Maybe Mex can give me a break on that when they have more bounce back time but not all 24? )
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Smitty77
Explorer
Explorer
Duplicate post...

Smitty77
Explorer
Explorer
If you find they're relatively close from these testing, then the KISS approach would be to connect them and treat them as one large bank.

If they're not close, then I'd probably treat them separately as two different banks of AH's. (Adding one of those fancy switches you mentioned, would make this much easier to swapping cables:)!)

Using and managing them as separate banks, you then know for sure how each one is doing, as well as you can optimize the charging for each bank.

Looking forward to what you find out after they rested:)!
Best,
Smitty

BFL13
Explorer II
Explorer II
Got the 10 hr test started. Maybe a problem already? I disconnected the three batteries yesterday after they were on their Floats, but this morning they still had a bit of surface charge it seems, so their voltages were not the same when I banked them to do the test. I had the 6G disconnected a little earlier than the other two.

6G - 13.16, Stark 1- 13.26, Stark 2- 13.22 by multi-meter. Banked it was 13.2 on Trimetric before 22.5a load applied. (at which it dropped to 12.6 "loaded")

Hope that won't matter for the final voltages after the 24 hr rest at 50%. Expect early individual 50% voltages this evening and finals Sunday evening.

A day sitting at 50% before recharging is not going to kill them. (If it does, they deserve to die!)

Another sign of ? is that when in parallel and on their recharges from the last trip and then on Float, the two Starks were at different temperatures. 22C vs 25C, eg, with Stark 2 the higher. Kept the 3C diff at different temps.

EDIT- battery temp is 15C both Starks at near 75% SOC. At 15C capacity is 95% of rated. 427 so my target is 214AH down. So my 22.5a is a bit high for the 20hr rate for that of 21.3 so must reduce to that or a bit lower to average out.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

MEXICOWANDERER
Explorer
Explorer
With AGM there should be near zero transfer. .15 volt difference is excessive. The high will be feeding the low to balance. When is operational stasis if that much potential is evident, grab your DMM set it for 10-amps and then find out how many milliamps are draining. Check it again an hour later. Imbalance still there?
what this "proves" is differences in chemistry. The closer the batteries pencil out the batter they will get along during the charge and discharge cycles as well as float.

BFL13
Explorer II
Explorer II
MrWizard wrote:
me.. i would connect them all together
use as one bank charge at 14.4v
top charge at 14.8v

float at 13.8v


I am kind of hoping that will work. I will still do Mex's procedure next couple of days to see if there is a problem arising from that.

I would still have the two solar sets (one 255w and three 100s) but would then put both controllers set to the same voltage on the one big bank. I could reduce to one converter.

No generator with the MH. (Just solar and alternator) So no 50-90s like before with the 5er doing 155 amps with a 55 and a 100 amp PowerMax. Only do charger at home with lots of time, so lower amps is ok.

The 100 pops a stick house breaker so likely just use the 55. (The 75 ADJ still does any 16v work like with the spare extra Wet 27s--that 75 is the only charger I have that can do over 15.5v.)

I am getting quite a collection of gear that still works I don't need anymore with the MH and no 5er or TC anymore. There might be a garage sale in my future! ๐Ÿ˜ž
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

MrWizard
Moderator
Moderator
me.. i would connect them all together
use as one bank charge at 14.4v
top charge at 14.8v

float at 13.8v
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

BFL13
Explorer II
Explorer II
wa8yxm wrote:
I did not follow the links but as SMALL differencer in voltage during the Bulk/Absorption statges would not scare me off. The float is the same and batteries in parallel form a "power commune" each according to its ability each according to its need.


I am more worried that the big 250AH might be more of a "floating/standby" type, and not be able to take high amp discharge (MW on inverter) or high amp recharging so well as the two 100AH batts, that can take that (as proven in service).

If banked, of course they share everything, so the impact on the 250 would be less than by itself. Yes, they share in proportion to their sizes in AH and will all keep the same voltages and SOCs while banked.

I would be giving up the advantage of being able to run down the 250 "house batt" and still be able to run the "inverter batt" without setting off its low voltage alarm (which is a real advantage), but OTOH, I have been with the 250 down to 50% and no way to recharge it right away, and still have bags of AH left in the inverter's bank, but unable to use those as wired up with no connection to the "house" 12v stuff.

I do have an extra couple of Wet 12v 27s to take along for extra house work to add to the 250 same as I did with the two 6s as "house" if the forecast is for no solar, but that is a pain. Six batteries.

I am looking at banking the three AGMs instead as a possible way to "get it all", with no solar for four or five days before going home. (No generator or shore power)

It has turned out that the typical AH usage makes this look possible, so I want to know if banking the AGMs is at least an option.

---I am adding to Mex's steps, that now they are all disconnected and charged up, I will leave them off Float like that till tomorrow and then get their resting voltages when full, to add to the later data of their resting voltages after being discharged to about 50%. Might mean something, and easy to get.

This might be a time for me to get one of those 1,2,Both switches some guys here swear by.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

wa8yxm
Explorer III
Explorer III
I did not follow the links but as SMALL differencer in voltage during the Bulk/Absorption statges would not scare me off. The float is the same and batteries in parallel form a "power commune" each according to its ability each according to its need.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

BFL13
Explorer II
Explorer II
Got them at hit the wall fully charged separately and on their Floats. I am always on a Float charge at home. Right now I float them separately but to the same voltage--13.8 with a temp adjustment if really hot or cold.

So next step would be to bank them and discharge to about 50%. My bank wiring would be the two 100s as a 200 in parallel with the 250 for 450 and put load/charge across between the 200 and 250 via Trimetric shunt for negs.

Discharge at 22.5a (20 hr rate) for about 10 hours and stop when AH are down 225. Disconnect all three and let them sit for 24 hours and check the three voltages.

What would it mean if they are not the same? How different is too different?

I can bank them today, do the 10 hr tomorrow, and the wait day Sunday, get the voltages Sunday evening.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

time2roll
Nomad
Nomad
Seems they will be fine while in use or on a float charge.
Disconnect if storing with no float.

(opinion only)

MEXICOWANDERER
Explorer
Explorer
You'd have to shut your system down for 24-hours to do the following.

1. Guaranteed hit-the-wall recharge everything.

2. Discharge to around 50% SOC

3. Disconnect between battery types

4. Measure voltage potential each battery after 24 hours disconneced

Lwiddis
Explorer II
Explorer II
"means usually getting the big one down to 50% while there is still lots left in the inverter's bank"

Certainly a 50% discharge is talked about mucho on this forum but its just a convienent number. Trojan for instance says on their Signature Flooded Line including T105, T125 and T145 that if you discharge to 50% you can expect 1,250 cycles but if you only discharge to 60% you can expect 1,500 cycles....almost an extra year of camping. I'd keep them separate, protect the most expensive battery first and switch when you get to a 60% SOC.
Winnebago 2101DS TT & 2022 Chevy Silverado 1500 LTZ Z71, WindyNation 300 watt solar-Lossigy 200 AH Lithium battery. Prefer boondocking, USFS, COE, BLM, NPS, TVA, state camps. Bicyclist. 14 yr. Army -11B40 then 11A - (MOS 1542 & 1560) IOBC & IOAC grad