Hi Happy,
As I have two charging paths from the engine, I used twin 100 amp remotely controlled continuous duty solenoids. The "activation" coil on each draws 0.88 amps. I have replaced the OEM 60 amp fuse with twin 50 amp auto reset circuit breakers.
The inverter is direct connected to the twin "house" banks. I use a Napa 1000 amp contacting 100 amp continues duty switches. (the type with a plastic "key")
All the switch live behind the driver's seat so I can disconnect on the fly.
I find I can run the 1200 watt water heater for about 20 minutes at highway speeds before voltage starts to sag on the engine side. I disconnect when I see 12.3 volts and allow the alternator to catch up for 30 minutes.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.