pianotuna wrote:
Hi Reed,
I don't always agree with BFL13, but I have a LOT of respect for the tests he has done for all of us. I'd be proud to call him a friend.reed cundiff wrote:
Well at least folks are being polite here, something that does not always happen on other fora.
Reed and Elaine
Solar autonomous for two years and delighted.
โMay-23-2015 11:33 AM
reed cundiff wrote:
Well at least folks are being polite here, something that does not always happen on other fora.
Reed and Elaine
Solar autonomous for two years and delighted.
โMay-23-2015 11:17 AM
โMay-23-2015 08:53 AM
โMay-23-2015 07:08 AM
pianotuna wrote:
Hi BFL13,
No I'm not saying that at all. A small bank needs more wattage because there is a much greater chance that it will dip below 50% state of charge.
-------------
The premise is that the two batt bank will be at 50% starting its recharge, so this is a deflection change of subject, not a response
-------------------
What I have consistently said is that as battery bank capacity rises the solar wattage per 100 amp-hours can be lower and may approach but not be below 60 watts per 100 amp-hours.
---------------
It is incorrect to say it "can" be lower. It is not some kind of choice. It IS lower if the bank is bigger while the solar amount remains the same at the AH required to replace daily usage
----------------
I have also consistently said that 150 watts per 100 amp-hours is a reasonable maximum wattage, because above 85% state of charge that is as much as the jars will accept.
--------------------
The premise is that the solar will replace the daily AH so it is understood the battery acceptance rate vs SOC at the voltage concerned will allow that recharge to 100%. So if that is the maximum per battery then that's fine, but not in dispute anyway
-----------------
Charging is not linear. Neither is discharging.
---------------
The standard V looking graph of that shows that the recharge is not linear for AH vs SOC and has that SG sag line too. BUT the discharge side shows a linear drop of SOC and SG. I don't understand what exactly PT is saying or where it fits in here
-----------------
If an inverter is going to be used or the user is a full time RV'er, then they may benefit from maxing out all available unshaded space, and they should ignore the 150 watt suggestion. They should NOT ignore the 60 watts per 100, unless they use bank switching (I do use it).
-----------------
It doesn't matter what the AH usage is composed of, inverters or LED lights. An AH is an AH and the daily AH usage from whatever cause is what we start with.
I am not including the battery requirement to be equalized as a solar requirement. PT keeps sliding that in as though the only way to equalize is with solar, so you must have enough solar to do that too.
I am saying the solar requirement is to replace the daily AH usage to get back to 100%. You don't need to equalize to get back to 100. Yesterday I got back to full baseline SG 100% before dark on solar alone with the last few hours of daylight in Float at 14.4 volts. (with 255W on a 458AH bank)BFL13 wrote:
So now you are saying the four batts will need more amps (and so a higher wattage array) than the two batts to cover the "higher" losses to do the same AH in the same time. This is a 180 in your story!
โMay-22-2015 09:17 PM
BFL13 wrote:
So now you are saying the four batts will need more amps (and so a higher wattage array) than the two batts to cover the "higher" losses to do the same AH in the same time. This is a 180 in your story!
โMay-22-2015 07:23 PM
โMay-22-2015 06:36 PM
Fisherguy wrote:
(This is starting to remind me of those infamous hotly contested converter threads...) :B
โMay-22-2015 06:14 PM
โMay-22-2015 05:04 PM
pianotuna wrote:
Hi BFL13,
No, the four battery bank will require more amp-hours to get to 100%.
You already know this from the generator days. No one does 90% to 100% using a generator because it is not cost effective because the charge tapers.
Since above 85% there will be no more than about 12.5 amps per 100 amp-hours going in. As the bank gets closer and closer to 100% there will be more and more loss. The loss may be around double for four jars vs two jars.
Whether that makes a difference in 'real life' situations or not I could not say without a careful experiment.BFL13 wrote:
Each needs the same AH to get to 100%. Assuming the solar can do that many AH that day, the time is the same, the AH is the same, so the amps must be the same.
Same amps, same size solar array.
โMay-22-2015 04:00 PM
BFL13 wrote:
Each needs the same AH to get to 100%. Assuming the solar can do that many AH that day, the time is the same, the AH is the same, so the amps must be the same.
Same amps, same size solar array.
โMay-22-2015 01:47 PM
pianotuna wrote:
Hi BFL13,
You need more wattage with a tiny bank because the depth of discharge is going to be greater.....
โMay-22-2015 01:31 PM