smkettner wrote:
You are comparing diameter instead of the cross section area.
With cross section area you can compare to a copper pipe or a solid copper bar.
area = (pi)rยฒ giving an exponential relationship between diameter and area.
Two wires next to each other one inch wide is not the same as a single one inch diameter wire.
On your chart use the area columns to add and compare.
โMay-24-2016 06:57 PM
smkettner wrote:
No parallel wire when roping a house right?
I mean if you ran out of #6 or #8 for the air conditioner you don't pull 2x #10.
I understand what you are saying with the #2 and #6. Just not my style.
โMay-24-2016 06:51 PM
โMay-24-2016 06:44 PM
grizzzman wrote:smkettner wrote:grizzzman wrote:
Crunching the numbers 14.6 volts 75 amps 14 foot (28 total using 6awg) shows a voltage drop of 5.68% (.83 volts) adding a 4awg to the 6awg would a bit larger then 2/0 awg and a voltage drop of 1.10% (.16).
It would likely be cheaper and more effective to move the converter. Can you?
2/0 133,100 cm
#6 26,600 cm
#4 42,000 cm
#2 66,500 cm
#6 + #4 looks more like #2 than 2/0.
http://www.genuinedealz.com/voltage-drop-calculator
OK how is this?
Inches. MM
#4 0.2043 5.189
#6 0.1620 4.115
0.3663 9.304
#00
2/0 0.3648 9.266
Hmmm not the same is it?
โMay-24-2016 06:29 PM
smkettner wrote:grizzzman wrote:
Crunching the numbers 14.6 volts 75 amps 14 foot (28 total using 6awg) shows a voltage drop of 5.68% (.83 volts) adding a 4awg to the 6awg would a bit larger then 2/0 awg and a voltage drop of 1.10% (.16).
It would likely be cheaper and more effective to move the converter. Can you?
2/0 133,100 cm
#6 26,600 cm
#4 42,000 cm
#2 66,500 cm
#6 + #4 looks more like #2 than 2/0.
http://www.genuinedealz.com/voltage-drop-calculator
โMay-24-2016 06:11 PM
grizzzman wrote:
Crunching the numbers 14.6 volts 75 amps 14 foot (28 total using 6awg) shows a voltage drop of 5.68% (.83 volts) adding a 4awg to the 6awg would a bit larger then 2/0 awg and a voltage drop of 1.10% (.16).
It would likely be cheaper and more effective to move the converter. Can you?
โMay-24-2016 06:04 PM
โMay-24-2016 05:59 PM
smkettner wrote:
I am not an electrician. Please refer to NEC but they don't always give details or explanations.
The text has been pointed out before but I cannot quote the section.
โMay-24-2016 05:24 PM
โMay-24-2016 05:03 PM
smkettner wrote:
I don't recommend parallel connectors and NEC is not real excited about it either except for very large transmission lines.
Frame is fine IMO as long as the connections are done well.
Good luck getting tinned marine #2 AWG into the WFCO connectors.
Might be rated #2 but maybe bare copper or SAE would fit better.
Just have fun should be first on the list ๐