I know someone with a Onan generator on his 38' DP. It has a 3600 watt LP generator that has a liquid propane line running only to the generator. So it takes in liquid propane, heats it and then uses it in the carburetor.
I don't know if the normal propane regulators can run a LP generator, let alone two. Modern code complaint tanks have a overflow safety valve inside them that should automatically shut off gas flow if a propane line breaks. However using propane at a rate in excess of 270,000 Btu's per hour can also trip the valve, even without a broken pipe.
There is 95,000 Btu's in a gallon of propane, while there is 115,000 Btu's in a gallon of gas. So automatically you will use about 20% more fuel on propane than gasoline. Lets say that the Honda 2000 where to use 1/2 gallon per hour, that is about 60,000 Btu's per hour, or about 2/3 gallon per hour of propane. You are pushing it to run the furnace, refrigerator and generator all on the same tank, probably better to use one tank for each generator? Many RV LP regulators are limited to about 130,000 or 190,000 Btu's per hour. If the generator comes with a regulator, then fine, it is probably rated at plenty of Btu's per hour for it's own use.
Fred.