Wiley123 wrote:
BB thanks for the suggestion, your right I could just do it that way and then all would be kosher.
Feb-19-2020 07:36 AM
Feb-18-2020 08:13 PM
Feb-18-2020 07:22 PM
Chris Bryant wrote:
I think you could run a neutral and install a sub panel feeding the outlets.
Feb-18-2020 06:35 PM
Feb-18-2020 06:01 PM
Feb-18-2020 05:55 PM
BB_TX wrote:That is the correct solution, otherwise you might have an interesting discussion with your insurance company if it ever caused a fire!!
To meet code you could change the outlet to a 4 wire outlet with neutral for the RV. Then make yourself a short custom dogbone 4 wire to 3 wire adapter for when you want to use the welder. That ensures you could never use both at the same time and the adapter would really be no big deal. Just leave it attached to the welder. Unplug one and plug in the other.
Feb-18-2020 04:13 PM
Feb-18-2020 03:55 PM
Feb-18-2020 03:07 PM
Feb-18-2020 03:05 PM
Feb-18-2020 03:04 PM
Feb-18-2020 02:56 PM
Feb-18-2020 01:42 PM
Wiley123 wrote:
I am out of room for extra breakers in my breaker box. I have a 220 3 wire outlet for my welder in the garage. Can I branch off of that outlet and install a 4 wire rv outlet if I run a separate neutral wire back to breaker panel?