I am considering purchasing a 50 amp cheater system to use when there is only a30 amp and 20 amp connection available at the site hookup. Have any of you used one? Any problems or issues I need to be aware of? Thanks.
Steve and LuAnne
2010 Fleetwood Bounder Classic 33U
Ford V10 Power Platform
Golden Retriever: KoKo
20 REPLIES 20

Retired_JSO
Explorer
Explorer
We have a few State Parks in southern Georgia we visit which has 2, 30 amp plugs in the pedestal. My adapter has 2, 30 amp male ends which allows us to run the entire coach on electric without a low voltage issue.

I have tried to use it at some Florida SP that only have a 30 and 20 amp plug. It will trip the GFCI on the 20.

When we had our fiver with 30 amp line but 2 A/C units. I used an extension cord hooked to the 20 amp and a dedicated circuit to our bedroom A/C. It worked like a charm everywhere we went. I have a friend that unhooked one of his A/C units from his wired 50 amp service and dedicated its power through an extension cord to the available 20 amp to get around our southern heat with both A/C units working.

jhilley
Explorer
Explorer
wa8yxm wrote:
diveman52 wrote:
Your method scares the hell out of me!!!!


Why, Everything is protected by proper breakers, Everything is heavy enough all connections are good and solid there is no risk beyond that which originally existed. The design is soild.

The factory wiring in the motor home.. Not so good.. I have had to upgrade and/or replace parts of it, but this modification is over built for safety.


At first glance it seems scary, but when you dig into what it is, it is actually quite safe. They are just emulating the way the RV is fed from the generator with two 120 volt feeds with one dedicated to the Air Conditioner. They are just breaking the AC lead and plugging it into 20 amp receptacle. In the OPs case he added a receptacle to plug in a heater.
2003 Winnebago Adventurer 38G F53 Chassis Solar Power
1999 Winnebago Brave 35C F53 Chassis Solar power
Handicap Equipped with Lift & Hospital Bed
1999 Jeep Cherokee Sport
1991 Jeep Wrangler Renegade

wa8yxm
Explorer III
Explorer III
diveman52 wrote:
Your method scares the hell out of me!!!!


Why, Everything is protected by proper breakers, Everything is heavy enough all connections are good and solid there is no risk beyond that which originally existed. The design is soild.

The factory wiring in the motor home.. Not so good.. I have had to upgrade and/or replace parts of it, but this modification is over built for safety.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

CA_Traveler
Explorer III
Explorer III
rgatijnet1 wrote:
Isn't a standard 50 amp plug using a total of 100 amps on the neutral with 50 amps on each leg?
The neutral carries the difference of the current on the 2 hot legs not the sum.

It's a 240/120V single phase circuit just like a house except the house might have a 200A rating.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

RoyB
Explorer II
Explorer II
This is a neat pictorial showing the typical camp ground pedestal and where the 50A and 30A/15A/20A sources come from.



These two pictorial show the proper way to test each of the three 120VAC sources...

50AMP Service (TWO HOT leads from each side of the 240V feed)

You can see 240VAC here if you measure from HOT1 to HOT2. Some upscale RV trailers indeed use 240VAC for some of the Dryer setup. In the regular wired RV 50A trailer two Power Panel ZONEs are used to tap off only 120VAC from each HOT1 and HOT2 legs of the 240VAC.


30A/15-20A service (ONE HOT lead from the same side of the 120V feed)

The highest AC voltage you will see here is 120VAC. The only difference between the 30A Connection and the 15/20A connection would be the rating of the circuit breaker (30A-20A-15A)


My attempt of showing how it works
Roy Ken
My Posts are IMHO based on my experiences - Words in CAPS does not mean I am shouting
Roy - Carolyn
RETIRED DOAF/DON/DOD/CONTR RADIO TECH (42yrs)
K9PHT (Since 1957) 146.52M
2010 F150, 5.4,3:73 Gears,SCab
2008 Starcraft 14RT EU2000i GEN
2005 Flagstaff 8528RESS

CA_Traveler
Explorer III
Explorer III
dsteinman wrote:
I am always confused about these adapters and I even have an electrical engineering degree, although I hated the power electrical class.

But, it seems to me that you have to make sure that the hot legs of the 30 amp and 20 amp circuits are out of phase with each other. Otherwise you would have the possibility of 50 amps on the neutral which would be fine for the motorhome and adapter, but I am not sure about the wiring in the electrical box.

Even worse would be using 2 30 amp plugs if both were in phase, which would then allow 60 amps on the neutral wire and overload all the wiring.

So, if someone can correct if I am wrong, I would appreciate it.

David
60A would be more than the rated 50A but it's not likely to be a problem and most certainly not if it's not a sustained 60A draw.

The significant issue for a CG (even if they don't understand the details) is that this adapter connects the 2 neutrals together which in turn causes the current in each neutral to be based on the impedance of each wire. This means that the maximum amp draw on a given neutral is no longer limited by the CB on the corresponding hot line. It's possible for example with a 30-20 setup the 20A neutral could be carrying 30A. This applies to the cheater neutral and the pedestal neutral. Also this is much more likely to be a problem when both hots are on the same leg vs connected to split phase legs.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

rgatijnet1
Explorer III
Explorer III
dsteinman wrote:
I am always confused about these adapters and I even have an electrical engineering degree, although I hated the power electrical class.

But, it seems to me that you have to make sure that the hot legs of the 30 amp and 20 amp circuits are out of phase with each other. Otherwise you would have the possibility of 50 amps on the neutral which would be fine for the motorhome and adapter, but I am not sure about the wiring in the electrical box.

Even worse would be using 2 30 amp plugs if both were in phase, which would then allow 60 amps on the neutral wire and overload all the wiring.

So, if someone can correct if I am wrong, I would appreciate it.

David


Isn't a standard 50 amp plug using a total of 100 amps on the neutral with 50 amps on each leg?

Dutch_12078
Explorer
Explorer
You're not wrong, but your first scenario of 50 amps on the neutral is within the design specs of the standard 50 amp 120/240 volt circuit used in motorhomes. The neutral is sized for the maximum 50 amps that would be seen if the entire 50 amp draw existed on one hot line, with zero draw on the other. An unlikely scenario at best, and one that also covers your second scenario, where 60 amps theoretically could be applied to the neutral, but in normal use is quite unlikely to occur. Even if it did occur, the safety margin of the wire rating would still handle the load.
Dutch
2001 GBM Landau 34' Class A
F53 chassis, Triton V10, TST TPMS
Bigfoot Automatic Leveling System
2011 Toyota RAV4 4WD/Remco pump
ReadyBrute Elite tow bar/Blue Ox baseplate

CA_Traveler
Explorer III
Explorer III
doxiemom11 wrote:
We have one and have used it at any campground that has a 30 amp plug. Ours is automatic and only boosts when it's needed. We are hooked up with one now and have used it all winter. We are running the water heater, frig and a 1500 watt heater (when it was cold) as our electric is included in our site rent. We do try not to overload though and do shut the frig off when using the convection oven or brew coffee. The cord on it is long enough that the actual device can sit inside a bay and is not visible. We purchased it when we were workamping for a summer and stuck on a 30 amp site that had low voltage and was causing problems. We couldn't run anything on electric, not even just 1 air conditioner. It worked there to solve the problem. Our unit was around $500
Your referring to a autoformer which is another useful device.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

dsteinman
Explorer
Explorer
I am always confused about these adapters and I even have an electrical engineering degree, although I hated the power electrical class.

But, it seems to me that you have to make sure that the hot legs of the 30 amp and 20 amp circuits are out of phase with each other. Otherwise you would have the possibility of 50 amps on the neutral which would be fine for the motorhome and adapter, but I am not sure about the wiring in the electrical box.

Even worse would be using 2 30 amp plugs if both were in phase, which would then allow 60 amps on the neutral wire and overload all the wiring.

So, if someone can correct if I am wrong, I would appreciate it.

David
2012 Fleetwood Discovery 40G
2012 Jeep Wrangler Unlimited
2019 Jeep Wrangler Unlimited

doxiemom11
Explorer II
Explorer II
We have one and have used it at any campground that has a 30 amp plug. Ours is automatic and only boosts when it's needed. We are hooked up with one now and have used it all winter. We are running the water heater, frig and a 1500 watt heater (when it was cold) as our electric is included in our site rent. We do try not to overload though and do shut the frig off when using the convection oven or brew coffee. The cord on it is long enough that the actual device can sit inside a bay and is not visible. We purchased it when we were workamping for a summer and stuck on a 30 amp site that had low voltage and was causing problems. We couldn't run anything on electric, not even just 1 air conditioner. It worked there to solve the problem. Our unit was around $500

RoyB
Explorer II
Explorer II
I am guessing you are referring to something like this... This one is available from pplmotorhomes


The first thing I notice is one of your 50A legs on the trailer side will have only a 30A capacity and the other 50A leg will have a 15/20AMP capacity. I also always worry about having a MALE connector out in the open that may be a safety issue in some instances causing a shock hazard. When you plug in the one side into the camp ground pedestal the other side of the male adapter is out in the open until you plug it in. It does not appear this adapter will have open HOT male connectors but just something to respect in case something is wired wrong inside the trailer.

Using this drawing from DMBRUSS showing where two 30A sources are connected to a 50AMP connector shows this same Scenario if one of the 30A connectors is substituted by a 15/20AMP connector...


The 50A side of this box would feed the two 50A Distribution Panel sides as shown here in this typical diagram


Other than GFCI issues mentioned above I don't see why this wouldn't work.

I would prefer having 30AMP capacity on both legs of the two 50AMP RV panel distribution and then you decide what is turned on at any given time to keep from tripping the camp ground pedestal circuit breaker.

Then I would run an extension cord to the camp ground pedestal and plug into the 15/20AMP service to run alot of things inside the Rv trailer to help with the possible overloading of the 30A service.

Be careful out there
Roy Ken
My Posts are IMHO based on my experiences - Words in CAPS does not mean I am shouting
Roy - Carolyn
RETIRED DOAF/DON/DOD/CONTR RADIO TECH (42yrs)
K9PHT (Since 1957) 146.52M
2010 F150, 5.4,3:73 Gears,SCab
2008 Starcraft 14RT EU2000i GEN
2005 Flagstaff 8528RESS

CA_Traveler
Explorer III
Explorer III
Some CGs don't allow the cheater cord. I have one that is rarely used.

I added a second circuit which plugs into a storage area plug or extension cord. I's used primarily for ceramic heaters.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

RayChez
Explorer
Explorer
I use mine all the time when there is only two thirty amp outlets. Mine works really good in the summer when you need to run both air conditioners. But you can only use it if there is nobody else in the adjacent parking spot that needs to use the second outlet. I use mine on two thirty amp plugs though.
2002 Gulf Stream Scenic Cruiser
330 HP Caterpillar 3126-E
3000 Allison Transmission
Neway Freightliner chassis
2017 Buick Envision