iwski wrote:
I have a new Champion 3500 inverter generator and a newly installed SurgeGuard 50A hard-wired surge protector. Upon connecting the generator, it would charge the batteries and power the ceiling fan (after the SurgeGuard start-up delay)
iwski wrote:
but when I tried the 15K A/C, the SurgeGuard faulted and cut power. Tried another approx 15 times, some with AC and some without (no load, only batteries charging). With the AC, usually it would run 3-5 seconds before the SurgeGuard would fault. With no load, the SurgeGuard faulted instantly sometimes and others times it would not fault and continue to charge batteries.
โAug-03-2017 07:19 AM
โAug-03-2017 04:10 AM
โAug-02-2017 04:52 PM
โAug-02-2017 01:43 PM
bob213 wrote:
Why not try a neutral ground bond plug and see if that helps. Easy to make for about $3.
plug