patchedup wrote:
Thanks. Sounds like battery is not enough or not charged enough.
โAug-14-2013 09:13 PM
โAug-14-2013 06:04 PM
โAug-14-2013 04:26 PM
MNtundraRet wrote:
The problem is that the OP was claiming about 5 hours out of 105 AH battery. I understand your calculation (I use similar) but the OP wasn't close with his 4 amp estimate for usage. That why I use a clamp-meter to check negative flow out of the battery for an hourly estimate on total use.
โAug-14-2013 04:05 PM
Chris Bryant wrote:
The 44 was based on 90% efficiency with a 4 amp 120 volt draw- a common ROT estimate of 11 to 1.
โAug-14-2013 03:14 PM
โAug-14-2013 02:33 PM
MNtundraRet wrote:Depends on the duty cycle of the freezer and the accuracy of 44(?)
As for the 44 amp guess, the inverter would have shut down in an hour or two..
โAug-14-2013 02:19 PM
โAug-14-2013 01:13 PM
โAug-14-2013 01:13 PM
โAug-14-2013 01:04 PM
patchedup wrote:That 4a freezer is at 120v, which draws TEN times that (40a) from the battery. As someone else said, I'm surprised you could run it that long.
I was figuring at 4 amp draw, i was drawing 4 amp per hr from the battery that had 105 amp to start out with.