MNRon wrote:
Cptnvideo - as 3Tons said, better than I did, my Magnum sees the genny as a defective power source because of the milliseconds of voltage droop when it becomes loaded. I have started the ACs on batteries and hoped the genny would take over. Unfortunately the Magnum takes a few second ms to qualify the new source, then when it tries to bring it in the genny voltage drops instantaneously and the Magnum kicks it out. If I run into this next time I might try limiting genny power to 15A, or 10A etc to see if that allows it to provide most of the power without significantly dropping. Weโll see.
3Tons - thanks, Iโve thought about just putting a Magnum bypass in to allow direct running of AC from genny. I think your solution is more elegant. Still I havenโt given up with futzing with current hardware instead of adding moreโฆ. Frankly not sure if I had spent more on a Honda I might not have been aware of this idiosyncrasy. Not sure if Iโll keep messing around or maybe make a hardware changeโฆ
I set my incoming to 18a when using my eu2200i generator and have no problem using it when needed for long run air conditioner time, I do not set it to eco mode on the generator. If you're getting the fault light and it's kicking your generator off try running just your fan on the ac unit for a minute or 2 then turn it over to air conditioner.
2 years ago when I was in SD and couldn't leave we had a hot spell that I would run the air conditioner off of solar/ batteries starting around 10am for 2-3 hours when the batteries got down to a SOC of 40% range I would switch over to the eu2200i generator. It will run for 4 hours + on a tank running the air conditioner. During that time the batteries would get fully charged at some point dependingon the sun. Once the batteries were fully charged by solar I would turn off the generator and run the air conditioner from solar/ batteries again for another 3-4 hours. By then it was getting cooler outside and air conditioner wasn't needed. This was a 2 week event off and on.
Most the time now were just using solar/ batteries and if it gets that hot we run to somewhere cooler if possible or just do what I posted above.
I'm over 7 years now on my setup with lfp batteries living fulltime off of them boondocking all of it mostly. Nov 4th or 5th of 2021 was the last time we were hooked to a power pole for a couple days traveling. Just amazing the punishment these lfp batteries can take.
Edit: I should note that I turn the charger off on the me-arc while using the generator for the air conditioner. Any charging of the batteries is coming from solar that isn't being used in load support. Also the front compartment is opened for fresh air because long heavy load runs will produce some heat from the inverter, you don't want to add the extra heat to the batteries if they're in the same area. I'll see cell temps rise to 93-95f and settle back to low 80s depending on the ambient temps for the evening.
My Me-Arc settings for the system....
Favorites (can be changed to personal taste)
F1_ Bat amps - PT ADC (present be produced)
F2_ AC output - 121 VAC/ 60.0 HZ
F3_ AC input - Amps= 15a (adjustable with incoming power)
F4_ Load amps - 0 amps AC
F5_ AC Amps - -2 amps
CRTL
01_ AC in Control - Auto Connect
02_ CHG Control - Multi Stage
03_ Gen Control - Off
04_ PT Control
โข a_ PT Chg CTRL 1 - Multi Stage
โข b_ PT Aux Relay - Control= Disengage
โข c_ PT Alarm - Control= Off
โข d_ PT Mppt Ctrl - 15 min sweep
METER
Inverting_ DC (present time reading)
01 DC Meters
โข a_ DC volts (present time reading)
โข b_ DC amps (present time reading)
02 AC Meters
โข a_ AC output (present time reading)
โข b_ Load amps (present time reading)
โข c_ Input AC (present time reading)
โข d_ Inv/ Chg amps (present time reading)
โข e_ Input AC1 (present time reading)
SET UP
01 System Set up
โข a_ Set Clock
โข b_ Screen set up (press select) _ Brightness (50%), Contrast (100%), Power save (1 min)
โข c_ Temp select - Fahrenheit
โข d_ Max charge- Amps 200 adc
โข e _ Link PT Chg - setting - yes
02 Inverting/ Inverter set up
โข a_ Search watts - Off
โข b_ LBCO setting - 12.0 vdc
โข c_ AC In time - 6:00am-6:00pm
โข d_ AC In VDC - 11.O-14.1 vdc
โข e_ AC In SOC - 80%-100% SOC
โข f_ Power up - Always off
SET UP INVERTING
03 Charger Set up
โข a_ AC Input - Amp= (can be set to available shore power/ generator incoming power)
โข b_ VAC Drop out - 80 VAC
โข c_ Battery type - Custom (with in here absorb voltage can be adjusted)
โข d_ Absorb done - Time= 0.1 hrs (minimum, can't be turned off)
โข e_ Max charge - Rate= 100%
โข f_ Max charge - Time= 12.0 hrs
โข g_ Final charge - Stage= Multi
โข h_ EQ Reminder - Days= Off
04 AGS SET UP - No AGS Present
05 BMK SET UP - No BMK Present
06 PT SET UP (Magnum pt controller follows Magnum inverter settings)
โข a_ Battery Type - Linked
โข b_ Absorb Done - Linked
โข c_ Maxed Charge - Rate= 100%
โข d_ Max Charge - Time= 12.0 hrs
โข e_ Bulk Start (press select)
- select Bulk Start, Daily / sun up= yes
- set Bulk Start, Volts= 12.0
- set Bulk Start, SOC= 80%
โข f _ PT Aux Relay - 10.0 to 14.0
โข g_ PT Alarm - 10.0 to 14.0
โข h_ Power Save PT - Display= 15 min
TECH
01 Temperatures (press select_ scroll)
- Inv BTS (present time reading)
- Inv TFMER (present time reading)
- Inv FET'S (present time reading)
- AGS Sensor 0ff
- ACLD Temp 32f
- PT BTS (present time reading)
- PT Inductor (present time reading)
02 Versions (press select_ scroll)
- Inverter: 1.2
- Remote: 4.0
- AGS: 0.0
- Router: 0.0
- ACLD: 0.0
- PT: 1.1
03 Inv Model - MSH3012H (3000w hybrid)
04 Fault History
05 Set up pin
06 Ext Control - No ext control
07 Show all - Menus= No
08 Load Defaults
The following parameters are for programming the ME-ARC Version 4 advanced control.
Setup 02B LBCO Setting: Volts = 12.0v
Setup 03C Battery Type: = Custom
Set Absorb Volts: = 14.1v
Set Float Volts: = 13.6v
Set EQ Volts: = 14.1v
Set EQ Done Time: = 0.1
Setup 03D Absorb Done Time: = 0.1 (minimum)
Setup 03E Max Charge Rate: = 100%
Setup 03G Final Charge Stage: = Float
12v 500ah, 20 cells_ 4s5p (GBS LFMP battery system). 8 CTI 160 watt panels (1,280 watts)2s4p,Panels mounted flat. Magnum PT100 SCC, Magnum 3012 hybrid inverter, ME-ARC 50. Installed 4/2016 been on 24/7/365, daily 35-45% DOD 2,500+ partial cycles.