MrWizard wrote:
yes common nuetral is a problem, and wired against code
you have too switch both HOT and Neutral, with the ATS for ALL power sources
that means switch both wires from generator, both wires from shore power
AND both hot and neutral from inverter
its the law , because its a Safety issue
โDec-19-2015 07:39 PM
โDec-19-2015 03:32 PM
smkettner wrote:
I crammed two relays in one box. If doing this today I would have the smaller TS by KISAE.
http://www.donrowe.com/KISAE-TS15A-Automatic-Transfer-Switch-p/ts15a.htm
โDec-10-2015 03:00 PM
โDec-10-2015 11:55 AM
smkettner wrote:
I ended up with two transfer switches to avoid the subpanel that would be hard to access.
If your loads are light you could just attach both to the one TS direct.
โDec-10-2015 09:51 AM
โDec-10-2015 09:24 AM
smkettner wrote:
So you are going to cut the hot bus bar in the panel?
โDec-10-2015 07:07 AM
โDec-10-2015 07:01 AM
โDec-10-2015 12:11 AM
MrWizard wrote:glamisduner wrote:smkettner wrote:
Transfer switch will not be able to backfeed the main panel.
You need a subpanel to break out the inverter items.
I don't understand, I don't want it to backfeed the main panel, that's the whole idea of not feeding the main panel with the ats. I just want to run one dual breaker off the ats output. Do I really need a whole subpanel for one breaker?
a box with one or two circuit breakers
can be a sub panel or a switch box, depending on how its wired
coming from the ats to a dedicated circuit Not powered by anything else
it is both a switch box and protected circuit at the same time
a sub-panel in RV context with a generator, shore, and inverter
is s selection of one or more circuts that can be powered by shore/gnerater switched by main ats,
and also powered by just the inverter
in other words that panel has multiple possible power sources
it isolates circuits that will be powered by inverter when other circuits do not have power
for safety things have to wired where there is absolutely no possibly of two power sources being connected to the same circuit
a sub-panel with mechanical interlock allowing only ONE choice, either/or is the safetest way of doing this
an ats choosing between two sources ( the oem breaker panel and the inverter ) can be used, as long as there is a CB between the output and the circuit
i have an ats on my fridge circuit, so it switches to a circuit from the breaker panel when the generator comes on
wiring can get confusing
and sometimes, its not clear what somebody is trying to describe
smkettner wrote:
If the generator is running and someone turns on the inverter they will both feed the same bus and the smoke comes out of one or both.
Yes you could switch some breakers manually but then why bother with the ATS.
If you just need one branch circuit then it could come right off the ATS.
Might get by with two circuits off the ATS depending on loads.
Have you mapped all five circuits?
-------
As for wire I would just use the max that the terminals are rated. I recommend battery cable over speaker wire.
I get my provisions here: http://www.genuinedealz.com/marine-wire/marine-battery-cable
Best value is to have them put the correct battery lug on one end and sealed with heat shrink.
โDec-09-2015 10:06 PM
glamisduner wrote:smkettner wrote:
Transfer switch will not be able to backfeed the main panel.
You need a subpanel to break out the inverter items.
I don't understand, I don't want it to backfeed the main panel, that's the whole idea of not feeding the main panel with the ats. I just want to run one dual breaker off the ats output. Do I really need a whole subpanel for one breaker?
โDec-09-2015 09:05 PM
โDec-09-2015 08:39 PM
smkettner wrote:
Transfer switch will not be able to backfeed the main panel.
You need a subpanel to break out the inverter items.