Usmcsousa wrote:
So quick Update, CG sent an electrician this AM. Of course he suggested underlying issues in my rig at first. Last Night I stayed hooked up to 30amp and all went well. The 50amp breaker was replaced and there was a massive colony of really ugly spiders living behind the breakers. Electrician says the Breaker was "weak" and the furry critters living behind there could have contributed to the strange power issues along with the weak breaker.I am hooked back up to 50amp and so far so good, will see what the night brings. Thank you all very much for your help!!!
โJun-11-2016 07:56 AM
โJun-11-2016 07:51 AM
smkettner wrote:Usmcsousa wrote:That seems reasonably balanced. Can you put water heater and fridge to run on propane only?
OK so one side is Front AC,TV,bathroom outlet,Dinet & sofa Outlets, Microwave
Second is Rear AC, Kitchen Outlet(coffee pot,)rear Tv,Bedroom outlets
Problem is probably the pedestal supply but this may help mitigate the issue during your stay.
โJun-11-2016 06:02 AM
โJun-10-2016 06:05 PM
Usmcsousa wrote:That seems reasonably balanced. Can you put water heater and fridge to run on propane only?
OK so one side is Front AC,TV,bathroom outlet,Dinet & sofa Outlets, Microwave
Second is Rear AC, Kitchen Outlet(coffee pot,)rear Tv,Bedroom outlets
โJun-10-2016 05:54 PM
โJun-10-2016 04:17 PM
MEXICOWANDERER wrote:
Circuit breakers wear out. A dual pole breaker has more krap inside to anneal and lean on a shovel. Most power pole connections are so corroded and ugly they would make Jed Clampett gag.
โJun-10-2016 03:20 PM
Usmcsousa wrote:dougrainer wrote:
I will bet you do NOT have 50 amp service. What you have is a 50 amp receptacle on a single 50 amp breaker with the 2 hot spades tied together. You need to do a simple voltage check with the 50 amp pole breaker reset and NOT plugged into your shore cord. Measuring the 2 hot spades at 3 and 9 o clock should yield double the line voltage(120 times 2 for 240). IF NOT this voltage and you get 120 on each 3 and 9 spade to ground or the neutral, then you have what is called "cheated" 50 amp service. This is NOT 50 amp service and you should not have to pay for this. Remember, 50 amp RV service is a TOTAL of 100 amps with 50 amps on each hot leg. Doug
I Wasn't aware of that,the Pole has two 50amp breakers bridged together, and showing 240v on the meter.
โJun-10-2016 02:27 PM
dougrainer wrote:
I will bet you do NOT have 50 amp service. What you have is a 50 amp receptacle on a single 50 amp breaker with the 2 hot spades tied together. You need to do a simple voltage check with the 50 amp pole breaker reset and NOT plugged into your shore cord. Measuring the 2 hot spades at 3 and 9 o clock should yield double the line voltage(120 times 2 for 240). IF NOT this voltage and you get 120 on each 3 and 9 spade to ground or the neutral, then you have what is called "cheated" 50 amp service. This is NOT 50 amp service and you should not have to pay for this. Remember, 50 amp RV service is a TOTAL of 100 amps with 50 amps on each hot leg. Doug
โJun-10-2016 02:23 PM
smkettner wrote:
Open the breaker panel in the RV. Most branch circuits should be labeled.
Each set of branch circuits will be next to a 50 amp main breaker.
L1 & L2 refer to the main breakers and then listed what is associated (connected) with each main.