drsteve wrote:
The furnace blower is supposed to continue to run after the thermostat shuts off the burner, until the heat exchanger cools off. Does it shut off immediately now? Because it shouldn't.
You probably need to reconnect the wire to where it was.
โJun-03-2017 08:33 AM
โJun-03-2017 07:37 AM
โJun-02-2017 12:03 PM
drsteve wrote:
That's not how you do it... check the voltage by touching the red probe to the hot side of the fuse and the black one to ground. You are simply placing the meter in series with whatever load is present on the circuit. This doesn't measure the voltage.
โJun-02-2017 11:06 AM
Chris Bryant wrote:
OK- the blue wire is the thermostat wire, it will not have power unless the thermostat is getting power and calling for heat. You need to measure the red wire, and the power on both sides of the breaker in the furnace.
The black wire likely hooks to the furnace outside and the left (looking from the outside), and from there goes to the breaker.
โJun-02-2017 10:54 AM
rejestered wrote:
However, I noticed that the furnace circuit itself is getting only 0.2V. I verified this with a multimeter by putting both red & black connectors into the slot where the 15A fuse goes.
โJun-02-2017 10:38 AM
โJun-02-2017 09:31 AM
midnightsadie wrote:
pull that fuse don,t just look some time oxidation sets in.clean it .
โJun-02-2017 09:29 AM
โJun-02-2017 09:23 AM
Chris Bryant wrote:
It probably does go right to the furnace, though it may power something else, as well. There is a circuit breaker on the furnace itself, and they do fail.
Where are you measuring the voltage to the furnace?
โJun-02-2017 08:51 AM
โJun-02-2017 08:44 AM
Chris Bryant wrote:
You have a 12 volt problem- nothing to do with 120 vac. The thermostat most likely gets power from the furnace, so if you sort the furnace problem out, all will be fine.
The 2 amp fuse is in the thermostat, fwiw.