SoundGuy wrote:3 tons wrote:
When generator is running, theres 125v, but only up to the inverter - the inverter for some reason does not ‘recognize’ the gennys output, so will not pass it thru to the campers circuits... Sounds like maybe a bad ATS inside the inverter...
More likely the ATS and / or inverter isn't happy with your EU2000i's floating neutral output. Have you tried bonding the genset's output?
Jul-22-2018 04:24 PM
3 tons wrote:
When generator is running, theres 125v, but only up to the inverter - the inverter for some reason does not ‘recognize’ the gennys output, so will not pass it thru to the campers circuits... Sounds like maybe a bad ATS inside the inverter...
Jul-22-2018 04:16 PM
SoundGuy wrote:3 tons wrote:
Update, I believe I’ve found a problem at the SP / generator ATS switch in basement - ATS lets shore power pass thru fine, but (per measurement) generator power is at about only 63v even though measured at generator’s output at 125v....
If you're not using a bonding plug on your EU2000i's output your ATS and / or SP may not be dealing with the genset's floating neutral output. Out of curiosity, what SP?
Jul-22-2018 03:08 PM
3 tons wrote:
Update, I believe I’ve found a problem at the SP / generator ATS switch in basement - ATS lets shore power pass thru fine, but (per measurement) generator power is at about only 63v even though measured at generator’s output at 125v....
Jul-22-2018 01:02 PM
Jul-22-2018 11:44 AM
3 tons wrote:
... but other variables such as elevation, ambient temps, length of run times (say beyond 30 min...) are seldom mentioned or even overlooked...
Jul-22-2018 11:32 AM
Jul-22-2018 11:27 AM
SoundGuy wrote:3 tons wrote:
This is the unit I have, and all works well when genny is not in Eco mode:
http://hypereng.com
Others who have installed the Micro-Air Easy Start have reported here on the forums that their Honda EU2000i will handle the start up load of a 13,500 BTU A/C even when running in ECO mode, which is obviously an advantage since the genset runs much more quietly in ECO mode. If yours doesn't that would suggest the Micro-Air might have been a better choice than the Hyper Engineering version.
Jul-22-2018 11:18 AM
3 tons wrote:
This is the unit I have, and all works well when genny is not in Eco mode:
http://hypereng.com
Jul-22-2018 11:12 AM
SoundGuy wrote:monkey44 wrote:
With the 2200i, does the Honda still need the "easy-start" item, or will it run the 13.5 AC unit stock from factory?
The Micro-Air Easy Start Soft Starter Kit does nothing for you once the A/C compressor has spun up to speed ... it's strictly intended to significantly reduce initial compressor start up current demand, allowing a 2K genset like the EU2000i to not stumble, go into overload, and shut down it's inverter output. The EU2000i is rated for maximum continuous load of 13.3 amps @ 120 vac, the EU2200i 15 amps @ 120 vac, so obviously the larger version will better handle the load of a running A/C, particularly when elevation rises above sea level and ambient temperatures are higher, both of which will degrade the performance of any generator.
Jul-22-2018 11:09 AM
SoundGuy wrote:SoundGuy wrote:
Personally I'd first invest in a Micro-Air Easy Start Soft Starter Kit for the A/C and see how your current EU2000i does.3 tons wrote:
Oops, I failed to mention that I did install the Easy Start (by Hyper Energy) last year but with little apparant positive result...
That would certainly raise concern, have you spoken to Hyper Engineering to ask why? The unit I'm referring to is a different unit, the Micro-Air East Start Soft Starter Kit which quite a few here on the forums have installed on their own A/C units, most larger than yours, and have reported great success, with an EU2000i easily starting their A/Cs.
Jul-22-2018 10:47 AM
Jul-22-2018 10:47 AM
monkey44 wrote:
With the 2200i, does the Honda still need the "easy-start" item, or will it run the 13.5 AC unit stock from factory?
Jul-22-2018 10:40 AM
SoundGuy wrote:
Personally I'd first invest in a Micro-Air Easy Start Soft Starter Kit for the A/C and see how your current EU2000i does.
3 tons wrote:
Oops, I failed to mention that I did install the Easy Start (by Hyper Energy) last year but with little apparant positive result...