If anyone is familiar with a Webasto diesel furnace, I have one that's acting up. It's the 45-50,000 BTU unit with the 287.962 12V silver control box. I have checked everything I know to check. The hi-limit switch has continuity, the spark sparks, the fuel solenoid clicks with separate 12V power and the blowers and pumps all work. However, the fuel solenoid will not open to allow the unit to fire. I can see that no 12V power is getting to it but am not sure what controls that. What I do know that I believe to be incorrect is that the C6 plug only shows 4.83VDC while all other ports have 12V. Is this an indication that the controller is not good and if so, is that the only way to tell or is there something I can do to test the controller itself before I have to spend $600+ for a new controller?