smkettner wrote:
You need sufficient load or battery draw to have voltage AT THE CONVERTER sag below 13.2 volts.
Not an easy task actually.
Far better to get a PD9260 or 55a IOTA with IQ controller.
To elaborate on that 13.2 business:
when you first apply a charger to a battery, there is an initial voltage spike from 12.x to 13.x. If the charging rate is high (amps vs AH size of battery bank) the spike will go above 13.2, can even hit 14 or whatever.
With a given charging rate, the next variable is the battery's state of charge. If it is higher in 12.x voltage, it will be easier to spike it above 13.2, so the idea is to have the charging rate just right and the SOC low enough that the initial spike is under 13.2, after which the battery voltage slowly climbs under the recharge in the usual way.
It happens that with the WFCO (and early model years PowerMaxs before they fixed that in 2011/12 ISTR) you need to get battery to just under 50% SOC and not hit it with too many amps so the spike is under 13.2 and it will go to 14.4v.
The reason smk is always saying you should try a 35amp charger instead of a 55amp is to get that charging rate down so that at 50% SOC it will go into 14.4 and not spike over 13.2 like it does with a 55 amper. However that still leaves you with a 35 amp charge instead of a 55. If you want a 55 rate and you can't get more than 13.6, you do need a different charger (of which there are several choices)
OTOH, if you want to keep the 55amp WFCO, you could try it on four batteries instead of just two. That halves the charging rate, so you might get your 14.4. Just takes a long generator run time to do a 50-90 on four batts starting at only 55amps!
๐ (I like to use 140amps to recharge my four 6s. I don't have a WFCO! I have a 100amp PowerMax plus a 40 amp VEC1093DBD and run both together from my Honda 3000)