time2roll wrote:
So 3 wire 240v split phase.... not 4 wire. Dang I would be hoping the conduit is large enough to pull a ground wire. Good luck.
Jul-20-2020 05:55 PM
Jul-20-2020 05:15 PM
Jul-20-2020 04:28 PM
rhochnadel wrote:
Eighteen years ago National Electric Code required the neutral bus and ground bus be separate, usually a single screw between the two buses would have to be installed to bond the two busses. Your barn panel should have a separate ground bus. Only the house panel should be bonded together. Talk to your electrician, ask him to correct it. You will be glad you did.
Jul-20-2020 03:38 PM
theoldwizard1 wrote:Thanks for the update.CA Traveler wrote:
It's OK. RVs don't bond utility power ground and neutral. That's done at the main panel and in your case the barn. The ground is a safety wire and bonding at the barn is consider safe.
WAS considered safe !
This was common practice until about 10 years ago (?) when the National Electric Code (NEC) changed and there can only be on bond in a system and it must be at the first disconnect. After that, 4 wires must be run to each distribution/breaker panel.
Jul-20-2020 03:24 PM
Jul-20-2020 02:47 PM
Jul-20-2020 02:30 PM
theoldwizard1 wrote:I stand by my recommendation to make it right.time2roll wrote:
At this point I believe it is best to separate the grounds to an independent bus in the barn subpanel.
If the installation was to code before the code changed your fine AS IS !
If you do not have 4 wires (2 hots, neutral and ground) going to the barn, disconnecting that bond would be dangerous !
Jul-20-2020 02:23 PM
CA Traveler wrote:
Interesting that earth grounding or not of a remote panel seems to vary. Local codes might be different.
Sjm9911 wrote:
It depends also on when the equipment was installed. Years ago panels only had one ground bar for both neutral and ground wires. It was the only way to do it. The ground is basically a back up to the neutral anyway.
Jul-20-2020 02:20 PM
theoldwizard1 wrote:CA Traveler wrote:
It's OK. RVs don't bond utility power ground and neutral. That's done at the main panel and in your case the barn. The ground is a safety wire and bonding at the barn is consider safe.
WAS considered safe !
This was common practice until about 10 years ago (?) when the National Electric Code (NEC) changed and there can only be on bond in a system and it must be at the first disconnect. After that, 4 wires must be run to each distribution/breaker panel.
Jul-20-2020 02:16 PM
time2roll wrote:
At this point I believe it is best to separate the grounds to an independent bus in the barn subpanel.
Jul-20-2020 02:13 PM
CA Traveler wrote:
It's OK. RVs don't bond utility power ground and neutral. That's done at the main panel and in your case the barn. The ground is a safety wire and bonding at the barn is consider safe.